2 x 100% - Lighting

Status
Not open for further replies.

NickParker

Electrical
Joined
Sep 1, 2017
Messages
455
Location
NL
The Specification says, "The emergency lighting system shall be redundant (2x100%)". The minimum average illumination level provided by the emergency lighting shall be 30% of the level provided by the normal lighting system.

Say, I have designed to meet the requirements of 30% of the level provided by the normal lighting system and I have the below questions
Do I have to duplicate the number of emergency fixtures to meet the redundancy? (or)
Do I have to supply the emergency light fixtures which can accept power from two different emergency sources? (or)
Do I have to supply the emergency light fixtures with inbuilt battery backup to meet the redundancy (or)
Do I need to provide ATS that can combine from two different emergency power sources; with this, Emergency light fixture which can accept one power source can be powered.

How do you interpret this specification?
 
I would ask the spec writer.
Also, is the 30% before or after the 2x100% is applied?

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
I agree, time for an RFI. All of your suggestions and waross' are possibly valid, but many exclude each other.
 