cdxx139,
naturally, our feel of what is more or less tedious does not have to be exactly the same. after long years i grasped rather firm feeling what is referent level of designer's engagement, and what goes beyond that, but that may differ in different parts of the world.
i did not understand you completely. i was talking about need to check air leaving temperature of FCU, but your are mentioning water reset temperature. if that is your water reset temperature, than air leaving temperature will go dangerously close to cold draft-feel temperature and the problem is exaggerated by the fact that all FCU's are oversized for heating mode, means they will reduce mean water temperature over surface very much. of course, heat transfer is not so simple process, and overall mean temperature will be reduced that way somewhat reducing heat transfer effectiveness, but if you are in position to use any simulation software, you can find that your air leaving temperature will come very close or bellow "danger threshold" for cold draft feeling.
and this problem is worst during lowest-load condition, being additionally emphasized in interior areas of commercial building that may have large cooling needs, but low heating needs.
my belief is that this problem is far from being simple, but, of course, we may have different opinions.
317069,
my understanding was that we are talking about central supply temperature reset, modulating on FCU level is mentioned in my previous post.