2 parallel generators sharing 3 GSU transformers fighting over voltage control

Status
Not open for further replies.

9wearSuave

Electrical
Aug 3, 2020
30
We have two identical synchronous generators connected at low side 13.8 sharing 3 GSU- 2 identical 138kV GSU's and 1 69kV GSU. Each generator has its own Basler decs 300 AVR and utilizes reactive droop compensation of 5%. Following a disturbance, the generators will cause MVAR oscillations one AVR must be switched to manual to make it stop. Is there a special configuration for 2 generators sharing 3 GSU's?
 
Replies continue below

Recommended for you

Better tuning or cross current compensation. Are they tuned the same way?

David
 
I do not see why the GSU arrangement would require anything unique. A few things to check:
-Is the droop is looking the correct direction? Are the droop CTs shorted?
-Are there overly aggressive power system stablizers?
-Are there any controld from SCADA or the plant control system that impact voltage control? I have seen oscillations at a plant when SCADA issues a new setpoint to only some units at a plant.
-It sounds like the 138 kV and 69 kV grids are tied through the 13.8 kV bus. Is there significant flow between the two transmission voltages via the generator bus?
 
At normal operation of both units, MVAR flows into 1 138 GSU terminal and also the 69kV terminal, and MVAR flows out of the other 138GSU terminal. It seems as if VARs are circulating on the 13.8 bus
 