gte447f
- Dec 1, 2008
- 815
I have a project with a 5" slab on grad. The concrete spec'd was 4500 psi, max w/c ratio 0.45, max coarse aggregate size 1" (but 3/4" is commonly used in mix design around here), air entrainment 4.5% or 5% plus/minus 1.5% for 1" or 3/4" max aggregate size respectively, and max slump of 5". The contractor wants to use a 2.5" diameter line pump to place the concrete, and has submitted an alternate mix design for the line pump with 3/8" max coarse aggregate, 5% plus/minus 1.5% air entrainment, and 4-7" slump range. The f'c and w/c ratio meets the original spec, but I am worried that the smaller aggregate and higher slump could result in increased shrinkage and cracking. Also, the smaller aggregate size should come with an increase in air entrainment to 6% plus/minus 1.5% according to ACI. Are my concerns about shrinkage valid or is this proposed alternate mix design OK? Could my original spec work OK for pumping through a 2.5" line pump (I suspect not with 3/4" to 1" max aggregate size)? Is it even OK to place concrete with a line pump like this, or should they be reserved got pumping grout? This is the second project recently where I have been asked to accept an alternate mix design to use a small diameter line pump. I think the contractors are just trying to be cheap. FYI, this slab is about 100'x36'.