Jan 30, 2017 #1 mohamed eldesoki Mechanical Joined Sep 22, 2016 Messages 8 Location SA CAN I CONNECT FIRE HOSE CABINET CLASS III AFTER THE ZCV OR I MUST FEED IT BEFORE ZCV ? AND PLEASE SUPPORT WITH REFERANCE
CAN I CONNECT FIRE HOSE CABINET CLASS III AFTER THE ZCV OR I MUST FEED IT BEFORE ZCV ? AND PLEASE SUPPORT WITH REFERANCE
Jan 30, 2017 #2 TravisMack Mechanical Joined Sep 15, 2003 Messages 1,776 Location US I'm assuming you are talking about standpipes. If so, then it must be independent from the floor control valve. Your reference is NFPA 14. Travis Mack MFP Design, LLC http://www.mfpdesign.com"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Upvote 0 Downvote
I'm assuming you are talking about standpipes. If so, then it must be independent from the floor control valve. Your reference is NFPA 14. Travis Mack MFP Design, LLC http://www.mfpdesign.com"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Feb 1, 2017 Thread starter #3 mohamed eldesoki Mechanical Joined Sep 22, 2016 Messages 8 Location SA thank you Upvote 0 Downvote