rhoudyj
Electrical
- May 8, 2019
- 5
Yesterday we had a power outage and our emergency diesel generator had to take over for a while. It had a mechanical failure a few hours in and we had to repair it. The generator in question is a bit older, about 25 year old, and is rated for 1MW. It supplies power to some computer HVAC equipment and approx 400kW of UPS load. It has about 650kW of load when all of the systems are operational. So anyway, we ran a 2 hour load bank test at 50% load and another 2 hour test at 100% in addition to a 100% step test with the same 1000kW bank. The generator passed these tests but when we simulated a power failure while connected to the original loads the field collapsed. I'm not quite sure what could be causing this. Do you all think it could perhaps be due to the VSR or an excitation issue? Did not get a chance to fix this before leaving. Still trying to think about what tests I'll want to do on the system later to try to diagnose this problem and any suggestions would be greatly appreciated.
Thanks,
Ronald Houdy, Jr.
Thanks,