1960's Flexicore Hollow Core Slab 1'-4"x8" Safe Load Tables 1
Clayton Hudson
4
Does anyone have the safe load tables for Flexicore hollow core slab panels made in the 60's? The building was built in 1966.
-Clayton
Thanks for the file. The size I am looking was not in there. I found some similar data for flexicore hollow core but it was for the 2' wide variant. I am still struggling to find anything for the 16" width.
I may have some info on 16" wide X 8" thick Flexicore planks. Let me check my library and I will get back to you ASAP
I checked my old copies of PCI Design Handbook - going back to the 1st Edition (1971) - and there are no load tables for any hollow-core products. They started load tables in the 2nd Edition, but all based upon 4' equivalent width planks.
I also checked out 'archive.org' that has a digital library of old books/catalogs etc - nothing there for Flexicore load tables.
I think you will be back to first principles - do some invasive probing and scanning to determine strand diameter and # strands per 16" wide plank, and knowing the section properties develop your capacities from scratch - make some relevant assumptions for f'c and fpu.
Above graphic is from PCI 1st Edition for Flexicore planks - similar to JAE's PCI link.
Found a Flexicore load table from 1958 in accordance with ACI 318-56:
A bit hard to read, so see attached PDF copy.
Unless you definitively know your tensile steel area (and/or have existing precast shop drawings) you are still going to have to verify your 'as-built' conditions via invasive probing etc.
We should get slideruleera to post this on his website.
faq731-376