rockman7892
I have a situation where the interrupting rating for the breakers on a 15kV metal clad switchgear lineup is aprox 64kA which exceeds the 63kA interrupting rating of the breakers.
The lineup is double ended lineup fed from (2) 70 MVA transformers with the breaker NC and a good bit of motor contribution fed from the switchgear.
I’m looking at a couple of different options to address this issue. One option is replacing the switchgear/breakers with adequately rated breakers however I’m not aware of any breakers with a higher than 63kA interrupting rating. A couple of questions I had
1) is there an option for a metal clad switchgear breaker that has a higher than 63kA interrupting rating or is 63kA the largest based on ANSI C37?
2) Would it make sense in this case to explore inserting a CLR in the tie breaker which would be perhaps a more economical solution for reducing SC duty?
3) Any other modeling techniques to perhaps eliminate any conservativeness in model impedance? Some things that come to mind are confirming cable lengths, looking at motor impedance model, and clarifying redundant motors. When two feeders from the gear are opened and motor contribution removed the fault duty drops below 63kA so to me that indicates looking at the motor modeling and feeders.