140% Recloser Coil

Status
Not open for further replies.
Replies continue below

Recommended for you

Somewhat- some major utility wanted 140X coils. Still don't fully understand why though.
 
I am not much familiar with Eaton reclosers but think 140% will be able to provide protection against overloads as well, to some extent.
 
How far past the rated KVA does the utility push their transformers for short time loading?

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Pole pigs can be pushed to 200-300% when feeding cyclic resi load- 105-125% commercial with varying loads- station transformers are typically 50-60% loaded at peak but off the top of my head 115% overload for the loss one unit on the basis a reasonable loss of life is acceptable on behalf that a mobile unit will be brought in or the peak load will occur only on the few hottest days of the summer.

Here is one POCOs over loading limits- see page 7 and 8:


 
Pole pigs can be pushed to 200-300% when feeding cyclic resi load-
Past experience is probably a driving factor when selecting trip coils.
When A/C is the major load on a very hot day there is not much diversity.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
I don't know the context in the application, but 200% coils are the standard for Kyle reclosers. As the 140% pickup coils start at 280A, my assumption would be to provide increased sensitivity downline of the recloser. I could also envision the application of them if I were stuck utilizing a hydraulic recloser for 3 phase with a trip coil size exceeding 280A.
 
Yup 200% is standard, but somehow X (140%) seems like an alternative option.
 