SprinklerDesigner2
As an example let's use Vikings VK460 residential horizontal sidewall sprinkler [URL unfurl="true"]http://www.vikinggroupinc.com/sites/default/files/documents/110205_0.pdf[/url]
If I have been interpreting this incorrectly over the years then at least I never did anything wrong.
We have an existing care home that requires retrofit and there isn't a space above the ceiling we can place our heads. Everything will have to be exposed below the ceiling so we're looking at exposed steel pipe.
The way I read the cut sheet is you must use the escutcheon as it is part of the listing and places the sprinkler a minimum of 1 3/16 and a maximum of 2 3/8" off the face of the wall or soffit.
Of course the distance down from the ceiling is a minimum of 4" and a maximum of 12".
The way I have always interpreted it is I can not simply run an exposed line placing my sprinklers 4" to 6" off the wall as allowed by NFPA #13 because we are not in NFPA #13.
The only way I can see doing this is run the line behind the wall doing whatever it takes to penetrate and place the escutcheon or install a soffit.
Can't use that; the entire house is a single dwelling unit. Trying to push it so each bedroom is a separate dwelling unit is just hoodoo to me...
But if we wanted to use quick response sprinklers we could but we would have to go to NFPA #13 and all it entails. Density, attic sprinklers and everything else that goes along with it.
Am I right? (I think I am 100% correct but just wanting to make sure).
NFPA 13R 2013 Edition said:6.2.1.3 Listed quick-response sprinklers shall be permitted to be installed in dwelling units meeting the definition of a compartment, as defined in Section 3.3, where no more than four sprinklers are located in the dwelling unit.