I'm looking at an old frat house that needs sprinklers. It's part of an overall "refreshing" of the building. They call for a 13R system. The basement and two floors up avg 2,800 sq ft and then a top floor is one big room where all the boys sleep, about 1235 sq ft. This is a typical frat design.
13R speaks of four head calculations in 600 sq ft compartments. The bldg has a 1 1/2" service in place and we would like to use it. A new dedicated service would be very expensive, $30K on the low end
Is there any way I can stay with the 4 head 0.05 gpm/ft calc in a room that big? Could the room be walled off into smaller rooms for this?
Alex Traw
Rainbow Fire Sprinklers
Albany, Oregon
13R speaks of four head calculations in 600 sq ft compartments. The bldg has a 1 1/2" service in place and we would like to use it. A new dedicated service would be very expensive, $30K on the low end
Is there any way I can stay with the 4 head 0.05 gpm/ft calc in a room that big? Could the room be walled off into smaller rooms for this?
Alex Traw
Rainbow Fire Sprinklers
Albany, Oregon