Dec 21, 2023 #1 doingwhat Electrical Joined Sep 10, 2013 Messages 21 Location US Hi all, Do we need to install a fire sprinkler head in a closet that is less than 24 square feet but without a closet door ? Does the closet (without s door) need to have a minimum lintel depth of 8 inches? Ray
Hi all, Do we need to install a fire sprinkler head in a closet that is less than 24 square feet but without a closet door ? Does the closet (without s door) need to have a minimum lintel depth of 8 inches? Ray
Dec 23, 2023 #2 cdafd Specifier/Regulator Joined Aug 18, 2005 Messages 2,953 Location US My answer for 13D or 13 R is No as long as you meet all of that section that applies,,,,, Door or no door And know the compartment definition https://m.youtube.com/watch?v=ms7pcjnXu-k Upvote 0 Downvote
My answer for 13D or 13 R is No as long as you meet all of that section that applies,,,,, Door or no door And know the compartment definition https://m.youtube.com/watch?v=ms7pcjnXu-k
Dec 24, 2023 #3 SprinklerDesigner2 Mechanical Joined Nov 30, 2006 Messages 1,276 Location US I am in total agreement with cdafd. Upvote 0 Downvote