QUOTE:
Generator; The sketch appears to show the generator neutral bonded to ground at the generator. If this is done you must use a 4 pole transfer switch and switch the neutral. END QUOTE
We are using an ASCO 7000 4-pole transfer switch per the EOR.
QUOTE: Then, when running on the generator the ground at the generator becomes the system ground. Only one connection is allowed between the neutral and the ground grid and the switched neutral is required to comply with this. You still need 5 conductors. 3 phase, 1 neutral and 1 ground. This becomes the system ground and if your code treats system grounds differently than equipment grounds you must use the system ground rules. END QUOTE
The EOR has these conductors. Code is NEC, we are still waiting for what year is applicable for this portion of the installation.
QUOTE - Alternate:
Remove the neutral grounding jumper at the generator. Use a three pole transfer switch and leave all neutrals solidly connected. The generator may now be treated as a piece of equipment and be grounded from the panel with an equipment grounding conductor as if it was a large motor. END QUOTE
I dare not suggest anything more :-(
QUOTE:
Shield grounding;
The normal treatment of an MV cable is to ground the sheath at the supply end and insulate it at the load end. The sheath conductors are generally cut off and taped over when the stress cone is installed. In each man hole, the incoming cables would have the sheath insulated and the out going would have the sheath connection brought out and connected to the equipment grounding conductor. Connection to a local ground rod is optional. An exception is concentric neutral cable. But the cable may have to be derated if the concentric neutral is connected at both ends.
Below about 100 amps underground and about 200 amps above ground it may be used without derating. END QUOTE
I need to thoroughly read this part. I have also attached the EOR's vault detail, I do not think it is as noted above.
QUOTE - Ground conductors in conduit;
Anecdote time, many generations ago our local Electrical Contractors Association did some testing. They found that 10 feet of steel conduit would act as a choke and limit the ground current to about 100 amps. They then bonded the cable to the conduit at each end and found that about 100 amps flowed through the conductor and the rest flowed through the conduit.
Comment, this is a magnetic effect, so aluminum conduit or PVC is electrically preferable to steel conduit for ground conductors. END QUOTE
We are using PVC but all penetrations through concrete are Steel, but much less than 10 feet, often less than 2'. However, I need to look at whether these nipples are bonded, should they be? *sigh*
QUOTE: If you must use steel conduit, remember that the grounding bushings may carry the major part of any fault current and exercise appropriate workmanship. END QUOTE
Again, I hope "they" are following this because I believe they view my posting any comments in an email as being an annoyance. Well, I guess if they are following the thread they can email me and let me know? I did send the link.
gare