allan789
Electrical
- Jul 17, 2010
- 10
We have a 11kV, GEC, 6.5MW motor which is connected via a gearbox and pinion to a ball mill. The motor is soft started by a LRS.
About a year and a half ago, April and again now yesterday the mill has gone for a start and has sat there not turning. It has sat there pulling 1800A until the protection eventually triped.
In all cases the motor and LRS has been inspected with nothing found. The mill was then inched by a seperate inching motor with no apparent mechanical windup or resistance. The mill was able to be restart after the inspection each time.
The LRS conductivity was measured at 14mS as compared to a design value of 12.7mS.
We have also had the motor reciently tested by a motor test company with no obvious abnormailties.
We are at a loss to what could be the cause of this intermitant fail to starts and any suggestions would be greatly appriciated.