GerH
Electrical
- Mar 18, 2003
- 48
A bushing failed on a 50/60MVA 110/20kV ONAN/ONAF transformer during FAT yesterday. The failure occurred a few seconds into the high voltage 50Hz test after the transformer tank had been on pressure test for about 16 hours. The porcelain surrounding paper insulation on the inner side of the bushing fractured, spreading broken bits on to the top of the windings and down the tank. No visible arc damage. The bushing paper surface which was under the broken porcelain is ripped along one side - presumably this was where the electrical breakdown occurred. Very reputable manufacturer. I have not seen this type of failure before. Should I be concerned or is it just one of those things that we should agree to replace the bushing, clean out the debris, retest and move on. I have asked for Tan Delta measurements on the bushing. Any comments appreciated.