Hi All,
We have a deep well water pump in our site and we have had more than 5 failures on it now. I am given the task of finding the root cause for the failures and give recommendations of what can be done to prevent future failures.
Here is the Pump Information:
1000 Horse Power Centrilift 725 HMI UT Motor
29 Stage HC3500 Centrilift Pump
4 Bag Sealing Section 6.75 OD
4160v Switch Gear with 469 Multilin Power Management Relay
Load information
Avg Discharge Flows of 1350 GPM
Avg Water Temperature of 95 Degrees Fahrenheit
Background:
I talked with the Electrical Supervisor and he thinks that the pump is being started lot many times ( 8 to 9 starts per day ) and that is the reason it fails. He argues that the pump fills the store water tank quick and so the level sensor shuts the pump. He recommends we do a lake and pump water into that and store so that we have less starts on that pump.
Other argument is that the inrush on the pump would be too high. Right now the pump is started with a DOL starter. Some recommend that we go with a VFD or a Soft starter to start and hence reduce the inrush and increase the number of starts. I think this is good than the lake option.
Also, do anyone have a recommendation of how to measure the sub transient and transient inrush current values of the pump during the start? I want to measure and see how much is the current rise. Wouldnt that help in the appropriation for VFD or soft start?
I know a little about pumps and hence whatever you guys give would be a valuable peice of information for me.
Thanks.
gokul
We have a deep well water pump in our site and we have had more than 5 failures on it now. I am given the task of finding the root cause for the failures and give recommendations of what can be done to prevent future failures.
Here is the Pump Information:
1000 Horse Power Centrilift 725 HMI UT Motor
29 Stage HC3500 Centrilift Pump
4 Bag Sealing Section 6.75 OD
4160v Switch Gear with 469 Multilin Power Management Relay
Load information
Avg Discharge Flows of 1350 GPM
Avg Water Temperature of 95 Degrees Fahrenheit
Background:
I talked with the Electrical Supervisor and he thinks that the pump is being started lot many times ( 8 to 9 starts per day ) and that is the reason it fails. He argues that the pump fills the store water tank quick and so the level sensor shuts the pump. He recommends we do a lake and pump water into that and store so that we have less starts on that pump.
Other argument is that the inrush on the pump would be too high. Right now the pump is started with a DOL starter. Some recommend that we go with a VFD or a Soft starter to start and hence reduce the inrush and increase the number of starts. I think this is good than the lake option.
Also, do anyone have a recommendation of how to measure the sub transient and transient inrush current values of the pump during the start? I want to measure and see how much is the current rise. Wouldnt that help in the appropriation for VFD or soft start?
I know a little about pumps and hence whatever you guys give would be a valuable peice of information for me.
Thanks.