Dear Mr. Melco001
I am looking at it in a different angle, for your consideration.
1. At the instant when the power failed with voltage and current dropped to 0V 0A; the motor generates a [back emf] with [decreasing voltage and frequency], independent of the load/the costing speed. This back emf decrease to 0V after say 3 cycles. If the power supply is switched back randomly, with source voltage and frequency, which if are NOT in phase with the motor generated back emf; an extremely [high current >LRA] and extremely high [mechanically torque] to pull the rotor back to the original running speed. These are detrimental to the breaker, contactor, coupling and motor.
2. When the power [voltage dropped] is <15% , no action need to be taken.
3. When the power [voltage dropped] is >15% but NOT zero, the motor may run into over-load (over-current). Tripping off the motor within say 3s should be fine.
Che Kuan Yau (Singapore)