Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

1000 hp Water Pump Motor Back Spin Protection

Status
Not open for further replies.

maintee

Electrical
Joined
May 3, 2004
Messages
7
Location
US
We had a situation recently where a 1000 hp 11.5 kV induction motor (full voltage start) was burned up because someone accidently tried starting the pump while it was spinning backwards. The operator was switching from one pump to another and was trying to perform a backflush of the pump intake by leaving the outlet valve open and using system pressure to force debris from the river intake screen. The motor started spinning backwards and making noise, so he panicked and tried restarting the motor.

The motor protection relays are of the old mechanical type and I would like to replace them with newer electronic types. Does anyone have any reccomendations for motor protection relays that could incorporate back spin protection. I see a GE Multilin 369 relay that advertises back spin protection, anyone have any experience with this unit or other ideas. I plan on interlocking the oulet valve to the motor starter, but want a backup protection on backspin.

Thanks for your time!
 
You are in the wrong forum. These guys are pretty smart about such things:
Electric motors & motor controls engineering Forum
(30198 members)
forum237
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top