Hi All,
I'm involve in a Hospital design where I have this scenario I never have done before.
10 isolation rooms being serve for a dedicated AHU. All air supplied into the rooms must be exhausted out of building. Min of 12 ACH. Negative Pressure to the adjacent area. (ASHRAE 170).
Since all supplied air must be exhausted, the AHU would be 100% fresh air.
The Outdoor temp design condition: 97F/79.4 DB/WB with a Winter o/a temp design condition of 73F.(caribbean).
Now, 12 "constant" (to keep the negative air balance) ACH at 55 F could over cool the rooms, in some conditions, therefore a reheat coil shall be provided in each room... So far so good.
Now my questions would be.
Will be neccesary to provide another reheat coil at the AHU for humidity control or just leave it to drop de air temp as required for deshumidification, and then reheat the air at the terminal units (CAV BOX with reheat coil)as mentioned above.
3.My control's proposal, is to set the leaving air temp at 55 F and provide a humidity sensor at the exhaust system main duct (common to all isolation room.)set at 60% HR. if the humidity goes above that value then valve will open to cool the air...Is this a good way to do it?.
My concern is, if the air is cooled too much wihtout being re-heated it might bring condensation in the duct..in other hand it dosen't make sense to me to have to reheat coils in serie...(ahu and terminals)
Please any advice will be appreciated...thanks,
I'm involve in a Hospital design where I have this scenario I never have done before.
10 isolation rooms being serve for a dedicated AHU. All air supplied into the rooms must be exhausted out of building. Min of 12 ACH. Negative Pressure to the adjacent area. (ASHRAE 170).
Since all supplied air must be exhausted, the AHU would be 100% fresh air.
The Outdoor temp design condition: 97F/79.4 DB/WB with a Winter o/a temp design condition of 73F.(caribbean).
Now, 12 "constant" (to keep the negative air balance) ACH at 55 F could over cool the rooms, in some conditions, therefore a reheat coil shall be provided in each room... So far so good.
Now my questions would be.
Will be neccesary to provide another reheat coil at the AHU for humidity control or just leave it to drop de air temp as required for deshumidification, and then reheat the air at the terminal units (CAV BOX with reheat coil)as mentioned above.
3.My control's proposal, is to set the leaving air temp at 55 F and provide a humidity sensor at the exhaust system main duct (common to all isolation room.)set at 60% HR. if the humidity goes above that value then valve will open to cool the air...Is this a good way to do it?.
My concern is, if the air is cooled too much wihtout being re-heated it might bring condensation in the duct..in other hand it dosen't make sense to me to have to reheat coils in serie...(ahu and terminals)
Please any advice will be appreciated...thanks,