Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

1 run in a two hole lug 2

Status
Not open for further replies.

tulum

Industrial
Jan 13, 2004
335
Just a quick questions... as a rule we purchase the right lugs for the cable (i.e 1 run of cable per phase gets a single lug, 2 runs gets a double, etc).

In the case of some of the 400A disconnects we purchased we received two hole mechanical lugs however, we installed 1 run of cable per phase... the switches are installed and the cable is run...

It is a nightmare to change all the lugs... if the cable is within the range of one hole of the two hole lug is it acceptable to use the one hole only?

Regards,
TULUM
 
Replies continue below

Recommended for you

If a two hole lug only need one hole wouldn't it come with just one hole?
 
I don't think tulum is taking about the mounting holes, but the barrel holes of the mechanical compression (vice crimp) lug.

Sure. Either you are not using the lug or disconnect to its capacity, or they anticipated possibilty of additional cable to correct voltage drop.

Either way your lug, load and cable will be perfectly happy.
 
A two hole lug and a two barrel lug are rather different things. Using only one barrel of a two barrel lug shouldn't be a problem.
 
This is a common situation on breaker & switches.
Torque & loctite or completly remove the unused set screw.
 
Thanks for the help folks.... pardon my langauage... two barrel is what I meant..

Regards,
TULUM
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor