PEMB Zee and Cee Purlins
NedHead
I'm trying to wrap my head around the design of light gauge Zee and Cee purlins in pre-engineered metal building design. I have the metal building systems book by Alexander Newman as well as the AISI manual and spec (newest edition of spec and the 2008 edition of the manual). Here's the set-up: fairly typical PEMB style building, 4:12 gable roof, 50'x90' long, steel frames at ~23' O.C. with Zee purlins spanning between frames. Standing seam insulated metal panel for the roofing, so I believe that means no diaphragm action (at least none you could really put numbers to).
With the sloping of the roof, you end up with weak axis bending in all the purlins, which normally would be taken out by diaphragm action, but in this case needs to be taken out to the steel frames through the weak axis alone. Even with really solid bracing between purlins (cold form channels at a reasonable spacing) you'd still be loading the purlins in the weak axis. As such I can't seem to get reasonable purlins to calc out well. I've seen 12" zee purlins spec'd at 20+' lengths and 4' spacing with higher snow loads than I'm currently working with on plenty of PEMB drawings, how do they do it? Are their systems using some diaphragm action they've arrived at through testing? Or diagonal metal strapping across the bays to take the load back the main steel frames (not a detail I've seen on any of the PEMB shops I have). Or is this just ignored when the roof slopes are low-ish
Wouldn’t the pre insulated panel act as a diaphragm
The types of insulated metal panels that I've been pointed towards by the architect all seem to have slide clips that don't allow for shear to transfer panel to panel. The few other IMP roof systems I've looked at all seem to be a similar situation which would negate any diaphragm action
Not really an answer but a comment. A lot of smaller metal buildings are not designed or certified by engineers, just "building designers" for companies like Mitek or others with proprietary metal building software. These structures get pawned off to the lowest bidder in such a way that all liability related to design criteria is removed from said designer. So, if you are wondering about how a metal building works, the answer is it probably doesn't.
That being said, rationally approaching the structure means that the hundreds of fasteners in the tin can 29 gauge diaphragm in conjunction with weak axis bending of the purlins must be the only way that load parallel to the frames get transferred from the roof , through the clips on the frame, into the frame and then through the moment frame to the (hopefully) engineered foundation.
When I design metal buildings I use a metal roof deck with actual capacities and analyze the connections from the deck to the frame. Of course, this is probably why I don't have a lot of metal building clients.
While a 4:12 may be a "standard offering" roof slope for many, a lot of PEMB roof structural logic was based on lower slopes (0.5:12 and 1:12). Somehow people have extended the design "logic" to 4:12s. I have seen many design calcs as if the purlins were 0:12 and then used on a 4:12 building. I have even seen it for a 6:12 once. Hanging point loads on 4:12s can be a more serious issue than 1:12s.
Zs have weak axis bending even on lower slopes.
I have not seen the panel thicknesses used in recent years, but minimum 26 gauge was a more common offering in the past. Rarely was anything less than 28 gauge used. 28 gauge was not a popular choice in earlier years. I have no idea how thin they are stretching things now.
First, who is the supplier you are working with for material sizes? Are you trying to piece together a PEMB from various component suppliers? If so, get their data first before you calc you own. There are so many more parameters involved in CFS than mill steel. Supplier criteria is not a constant.
If your roof panel is on "floating clips" for expansion, to my knowledge it has never been modeled as a diaphragm. Only a direct screw down is used for a diaphragm, and it is limited.
Also, are your Zs simple span or continuous? That may make some difference.
Wayne, that's quite helpful to hear, if only as reassurance that I've not lost my marbles and the PEMB purlin schemes I've seen may in fact not work. I'm looking at either adding in metal deck for roof sheathing or providing a hot rolled shape for my eave beam/strut that I can brace all my purlins to and deal with the weak axis loading that way. The stiff beam at the eaves feels a little more palatable than the full steel decking, not sure how the costs would actually shake out.
Ron, that is also helpful and makes sense. We've looked at other PEMB components before and could never get those down to the sizes the PEMB companies say work, so I guess I'm not surprised that's the case here as well. That is essentially what I'm doing. I've been basing my designs off a supplier out of a specific supplier out of PA (project is in the Northeastern US). As for other parameters for CFS suppliers, I assume you're referring to the slew of slightly different section geometries? That seems to jump all over the place supplier to supplier. I've run my Zees assuming continuous and will design for the laps at the rafters. Thanks for confirmation on the lack of diaphragm action.
jhnblgr, that image looks very similar to the IMP details I've seen, and lacks any attachment panel to panel
I have seen PEMB use additional clips or plates at the frames to brace the purlins. They will call these anti-roll clips. Then at the eave, they will put in a lot of braces at ~4'-0" spacing then continue it back 3 or 4 purlins to distribute the loading.
You have to use specialized software to make PEMB design worth the money. https://mbsweb.com/
GC_Hopi - Those anti-roll clips only handle the weak axis load once it's been carried out to the rafters along the length of the purlins. It doesn't help the purlins along their length at all. As for the braces at a tight spacing along the eave, those only do any good if your eave beam is stiff enough to take the weak axis load of all your purlins combined, otherwise you don't get weak axis strength out of the braces unless you were to add in diagonals and build a truss of some sort.
I'm a PEMB guy.
For wind loads, there shouldn't be any weak axis load because that load always acts normal to the roof plane.
Snow load is another matter. That will have a component of force normal to the purlins and a component normal to the roof panel. Standing seam roofs are always through fastened somewhere along their length. Usually at the eave but can be at top or midspan. different companies handle it differently. One company I know of had a matrix based spreadsheet to check roll force to see if the purlins can take the load normal to the panels. I've also seen a detail with cold formed member installed normal to the panel.
It wouldn't be surprised if they don't show their method clearly on approval drawings but there is zero chance that a company based in the northeast doesn't have some way of accounting for this snow load. If they did, they'd be out of business the first winter they were in operation.
Correct with the anti-roll clips the purlin still has to have enough strength to span between them so that limits that amount of loading it can take. Also correct with the bracing you are making a truss to resist that weak axis load so you can take a lot more loading and you are summing to load as you go towards the eave. That means close to the ridge the purlin might work on its own then can you work toward the eave you add zee members between the purlins as bracing to cut the span then when you hit the eave you put in your purlin/truss bracing.
Don't underestimate the amount of bracing that is necessary to get some of the steep and/or heavy snow load roofs to work. Using CFS is similar to wood design in that manner where you might end up with bracing on the whole roof. I have seen designs where all the purlins have bracing at 5'-0" and truss bracing at 5'-0" on the eave.
Here is an example of one bay with heavy bracing
