Attachment to Existing Terra Cotta
gtrocks
Has anyone ever used Hilti HY270 to attach a shear connection to an existing Terra Cotta exterior wall? We are supporting about 1000#. Hilti lists "hollow clay masonry" and some capacities, but I would guess that Terra Cotta is not what they mean. We were expecting the backup to be concrete masonry, not Terra Cotta. Thanks
I'd be hesitant to depend on Terra Cotta for anything structural - just me being a big chicken.
I understand it has moderate compressive strength but for shear and tension it's probably closer to dried snot.
I would probably specify in-situ testing in a variety of panels with a few different conditions (e.g. some centered, some closer to edge, etc.). That's our usual course when we're outside published tables, which is not an infrequent occurrence. If you don't have that opportunity at the design stage, then increase number of anchors by some margin and write the testing into the contract. Be sure to let the owner / client know that the spacing is contingent on satisfactory field performance and that if the field test does not pass muster, you may not be able to do what they envision. Also, to avoid cancelled construction contract fees and all that, write it such that a mock-up (with field testing) occurs prior to everything else and that the contractor shall include in their price the possibility of termination due to lack of feasibility or similar.
What about busting out some faces and grouting it first?
This is what we always do with terra cotta. Never take the risk of just attaching to hollow units. Usually you can kick them open with your foot.
Also, correct me if I'm wrong, but I thought the "clay masonry" section of the Hilti catalog went away. I don't recall seeing it in the HY-270 chapter. I remember referencing the old HY-20 or HY-70 books to find that info years ago.
Sort of. The latest guide says to refer to the 2022 version for brick.
And that, from what I can tell, can be found here: North American Product Technical Guide: Version 22
I found it. It was the old HY-20 catalog from when I first started working. Had specifically clay tile info. But we spoke to our Hilti rep after they switched to HY-70 and HY-270 and he said something like they stopped testing on clay/ providing values since it was so rare.
Link here for the 2011 catalog: https://files-ask.hilti.com/original/7v/7vmplgc2kc.pdf
See pages 7 & 218.
WHAT!?!?!?
There's an entire sector of the industry devoted to restoring buildings made of these materials. I realize it's not a huge part of their business, but it was an under served market even when they were serving it.
What is the condition of the terra cotta? Any cracks?
What is the age of the terra cotta?
How is the terra cotta connected to the backup masonry?
What is the condition of the anchors between the terra cotta and the backup masonry?
Where are the new anchors in relation to the terra cotta joints"
What is the condition of the backup masonry?
Personally (and from several bad experiences) I would not rely on the terra cotta to support any loads other than its self-weight.
This is plan B when the face shell bursts when they try to make a hole with the hammer drill.
Then why are you asking all of these questions? :)
WHAT!?!?!?
I forget the exact details since it was a while ago, but what I remember is that it just wasn't worth it for them to add that base material for the new anchors. It's probably such a low percentage of use for their anchors compared to CMU and Concrete probably wasn't worth the effort to provide values and certification for clay blocks.
