What kind of induction generator is this? If it is a normal squirrel-cage machine, you don't need any separate connection for providing excitation. You can also self-start squirrel-cage machine without grid supply by using capacitor bank between generator and grid. Rotor residual flux will cause a resonance in LC circuit and self-start the magnetization. After that, generator takes the excitation from the grid through the stator terminals. So yes, you need excitation power still from the grid (which means lower power factor), but not any additional connections for that. If you have a constant turbine speed, then squirrel-cage machine could be used.
If it is a so-called soubly-fed induction generator (DFIG), you will have a normal three-phase winding also in the rotor and you need to supply magnetization energy externally all the time. I don't think you can start such machine without grid power. If you have varying turbine speed, then you should use this, but you will probably need some power electronics to supply rotor magnetization (its frequency must vary)
About the inrush current.. Are you sure you are not confusing to locked-rotor current of an induction machine, which can be up to 10 times the rated current? This applies only in direct on-line start, when you connect the generator to grid from zero speed (you have slip = 1 at first). But if you drive the machine close to synchronous speed with turbine, and then close the breaker, I don't think you will have such high current.
