  1. wareagle

    Maximum lenght of a overhead line

    The Wiki article mentions line losses in a transmission line. Losses in watts = I² x R. For a fixed length of line the resistance R is fixed. For a fixed resistance, the heat losses dissipated is = V² x R. Therefore is you are using selected conductor size and a given acceptable loss, the...
  2. wareagle

    Unbalanced load in 3 phases system

    hisham It sounds like you are caught up in that old example the flow of electrical current is like water flowing through a hose. Nothing could be further from the truth. If you take a simple circuit like a lamp and connect the two wires from the lamp to 120 volts the lamp lights. At the time...
  3. wareagle

    neutral return current on single-phase system

    You obviously have other paths being used. Does you local code allow the water pipes to be used in the grounding system? 100 amps is a lot on a single phase line. I am surprised that you are not receiving electrical shocking complaints.
  4. wareagle

    Long conductor sizing for motor

    check this information first http://findarticles.com/p/articles/mi_m0BPR/is_10_22/ai_n15766075/?tag=content;col1
  5. wareagle

    distribution lines

    I agree with both of the previous posts. The owner of the line will have requirements that you must follow. Did you have a distance in mind?
  6. wareagle

    Options for reducing through flows

    Could you give an example of a through power flow ?
  7. wareagle

    Dunki's sqrt(3)*rated voltage motor life rule of thumb

    Quote waross "So when a motor is operated at the star voltage rather than the delta voltage the life expectancy is 1/700 or 0.14%." I don't follow your math.. I would say the operation at the voltage stated would reduce the life time hours = 700/expected lifetime hrs. I am not familiar with...
  8. wareagle

    Transformer Percent Impedance

    %Z is not the transformer impedance but you can obtain it form the transformer information. The links below explain it in detail. www.jcmiras.net/jcm/item/117 www.jcmiras.net/jcm/item/116
  9. wareagle

    Securing 4160 cables inside of MCC.

    I would not think a water hose clamp would be listed for this purpose. Why not use a nylon strap?
  10. wareagle

    160MVA Load

    Have you calculated the amperage at 66 kv and 220 kv. Looks like you need a generation plant in the back yard. At 220 kv calculate the VD at max load. Then decide what you need to do.
  11. wareagle

    Need some advice on becoming an electrical power systems designer

    Are you speaking commercial/industrial design or something like utility power distribution? They are different. I google your question and found the following: http://www.google.com/search...
  12. wareagle

    Conduit Drains in Crushing Plant

    Good answer Bill. You slapped the MBA and made it seem like kiss. I can't believe there is much difference in cost for either A or B.
  13. wareagle

    VSD Transformer output voltage

    Stanley I would get my voltmeter and measure all of the voltages for myself. Scotty has one possibility, but these reading are crazy.
  14. wareagle

    Marine Shipboard Cable Termination Ampacity

    This may help http://www.summit.com/industries/marine/downloads/marine-cable-brading-and-cutting/Drilmar/Drilmar_SCPDC_TypeP600.pdf