Plastic or metal IBCs? That's the big question.
The Scheme is based on the liquid's classification, if the liquid water-miscible or not water-miscible, the container's material of construction and its volume. Scheme A-E are limited to rack storage. An IBC under NFPA 30 is not a Container...
The only provisions for a ramped walkway are in the International Building Code or the Life Safety Code and are limited to Means of Egress. I'm not aware of a provision for your described situation in the National Electrical Code but I will warn you I have limited experience with the NEC...
The fuel level in a fire pump is gauged. This means one uses a sight glass, a liquid transmitter connected to Human/Machine interface, or a simple clock gauge based on the tank.
Your client brought a high-risk fire hazard to a jurisdiction. Your responsibility, based on the local fire code, is to provide a reliable water supply. More than likely you will need to provide a static tank and water supply.
I cannot help you unless you provide the building code governing...
OH G2 because of the idle pallet storage. Be careful if the distillery performing canning operations. Automatic canning equipment commonly will assemble the palletized load. Part of this process involves inserting a 1/8 inch sheet of HDPE of PE film. An assembled pallet load can have > 15%...
I would classify it as Cartoned Unexpanded Group A plastic unless test data demonstrated the heat release rate is consistent with similar Class III commodities.
It depends. NFPA 30 requires a means of containment and diking from a petroleum storage tank containing Class I, II or III liquid. The 2021 International Fire Code and NFPA 400, in certain cases, requires the design of an outdoor secondary containment to contain a specified volume liquid based...
Review Chapter 6. Nothing in the provisions prohibit the installation of a dispenser on top of the AST so long as it meets all of the NFPA 30A Chapter 4 provisions. Note that Section 4.3.6 only allows for openings at the top of the AST.
Section 6.3.4 doesn't require require a remote dispenser...
You're not using the correct standard. If the aboveground storage tank installation is for motor vehicle fuel dispensing, the design should be based on NFPA 30A.
Let us know how the internal inspection of the 113 year old pipe goes.[bigsmile] I appreciate the passion of the Historical commission members but you're correct about the issues and solution. Your client has a GA Fire Code issue and you're tasked with solving it. You may be able to leave the...
The Times newspaper in Gainesville, GA has reported that the CSB found tools in the area where one of the new flash freezing units. Again, avoiding speculation, this finding raises more concerns about the employees understanding of LN2...