Recent content by rovineye

  1. rovineye

    Scotchkote replacement

    We have used 3M Scotchkote Electrical Coating for years, mostly to coat vinyl tape at low voltage motor terminations and the like, to seal and prevent unravelling. Now the sale has been halted in about 10 states due to very high VOC content. Any suggestions for a similar coating product? I...
  2. rovineye

    Coating

    The sale os Scotchkote has been halted in about 10 states due to issues with the VOC content, as of June 1, 2011. Bummer.
  3. rovineye

    Earthed and Unearthed Systems in Ships

    It isn't so much the cost of the equipment as the amont of equipment you need, depending on your distribution system. For instance, with a earthed system, you can easily have wye xfmr with neutral 120/208 system with less cable, transformers and panels.
  4. rovineye

    What's this fuse symbol?

    I would agree with that. But it isn't the case. I think the schematic is in error, but wanted to see if there were other possibilities.
  5. rovineye

    What's this fuse symbol?

    All I know is that it is a slow blow fuse. Anyone recognize it? The fuse isn't in any kind of a rack-out assembly. I've never seen this before.
  6. rovineye

    Lug Voltage rating

    Quite true. My termination kits do specify the lugs that can be used, even when not supplied as part of the kit.
  7. rovineye

    Lug Voltage rating

    The few of my data sheets that do list a voltage rating all list 600 to 35kV. See the link to Scotchlok. T&B is the same on my glossy sales brochure, and Burndy is silent. I don't have any Sqr D info.http://multimedia.3m.com/mws/mediawebserver?mwsId=66666UuZjcFSLXTtMxMa48z6EVuQEcuZgVs6EVs6E666666--
  8. rovineye

    ILO Rules for accommodation on newbuildt vessel

    Did you check ILOLEX database for the requirement? If there is a requirement, you can be sure it does not mean a towel rack. Pain in the ass if it is there. Add a hundered bucks per stateroom and a few hundered watts. Not that there is room for onein most heads...
  9. rovineye

    Diesel Generator Coupling

    Bill you are right on two counts! #1. From the engine manufacturer: "Research has shown that the requirements were implemented as an aid in analysis of torsional load optimization of the rotating system." #2 (to make me go away) "That analysis being complete, the requirement is now...
  10. rovineye

    Diesel Generator Coupling

    Theblacksmith; Yes I have asked, but no reply yet. Waross, That is the interesting aspect to me. The instruction come from coupling OEM, and is identical for both 8 and 9 cylinder engines, which both mate up with identical generators. 11500 kVA, 14 pole.
  11. rovineye

    Diesel Generator Coupling

    No, the two have never met. Both are independently balanced at the factory and I am 100% certain that the generator has no planned balance offset.
  12. rovineye

    Diesel Generator Coupling

    My coupling and alignment instructions for my diesel generator set call for #1 cylinder to be TDC and the generator rotor positioned with the north pole (@ the shaft key position) also TDC. Why?
  13. rovineye

    At what size do emergency / service generators require pre-lube pumps

    The smallest gen sets I have dealt with were about 1600 kW (900 or 1800 RPM), and at that level the generator bearing required pre-lube, but not the engine.
  14. rovineye

    Popeye's electronics

    Maybe you can use VCIs. Vapor-phase Corrosion Inhibitors are foam emitters through which the corrosion inhibitor is slowly released and moisture and air pollutants can enter to be absorbed. It provides long-term protection against corrosion even in the presence of adverse conditions including...
  15. rovineye

    The use of DC mains in US Naval Vessels circa WW2

    Maybe they wanted DC on the reefer ship to control speed of the compressor motors. Similarly on the supply ship for the crane or elevator motors.