I have a regulated power supply 60VDC at 10A which I need to reduce to 42VDC
Can anyone please point me in the right direction. I know about 3 term regulators but most have a limited current rating
Thank you all
Its very hard to get information during the planning stages of a project from manufacturers, especially when asking for characteristics and dimensions. Plenty of brochures around, and lots of info on standard 2 and 4 pole items. Hence the call to this forum. Thank you for the...
Would anyone know of a good source of commercially available low pass filters to reject 475HZ ripple frequency into 230AC 50HZ 60A loads? The ripple frequency is upsetting LEDs over a wide range of households
Closed loop stepper motors usually have 1000 segments per rev, but with quadrature encoders you can get up to 4000 positions per rev.
Micro stepping can be used on 1.8 deg stepper motors. This holds the position between 1.8deg using current control
The max is 51200 pulses per rev but you don't...
I can understand using any microstep value to get you to a known encoder position. But that implies that you can only accurately hit 1000 divisions per rev (or maybe 4000 with quad encoders) to be held in closed loop position by the encoder
If you want to do 99.3 divisions you can microstep...
Now to answer your question. Usually the kW output is near or the same as as the motor nameplate kW, usually the issue is the efficiency of the turbine it is connected to. I had one client who ran the hydro to the limits of the temperature rise in the stator, which gave him another 5% over...
I have put in over 8 MW of motors as generators ,usually in the range of 500kw to 1MW, including synchronous motors into hydro schemes. However there are some issues that you need to consider
a) Any induction motor running as a generator does so with leading power factor. That is to say the...
KCad
https://kicad-pcb.org/
Free
The main problem is that the online component libraries are not easy to navigate but it is easy to generate your own schematic and footprints of items as needed...
https://www.omc-stepperonline.com/download/CL57T.pdf
This is the best document I can find on setup, but doesn't have any information on how it all workd
Perhaps not the place for this question but I cant find the answers anywhere!
Small closed loop controllers such as the CL57T and LCDA257S allow settings from 800 to 51,200 pulses/rev from the encoders they connect to. There is only two encoder connections on these modules.
Most of the small...
Isolate the generator and then manually close the incomer to the transformer
This should liven all of the Pts and show whether the running and incoming are phased matched
I do this for all synchronising checks
Thanks for that. Yes the question has arisen because of embedded generation, and an open 11kV line feeding a transformer up a hill.
The problem is that nearly everyone you talk to knows of the isobus concept and unearthed connection, but there are many instances (hydro in particular) where the...