Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by redha123

  1. redha123

    TRAINING IN EUROPE

    Thanks "polleke" for your respond
  2. redha123

    TRAINING IN EUROPE

    hi i'm loocking for europen training about 5 days maximum concerning cathodic protection : France, Belgium..... help advices....
  3. redha123

    Corrosion monitoring probes

    Hi after 3 years of use we need to change our probes (ER,LPR ). my question is shall we bey all the probe or just the insulator and some o-rings ? did you extracted probes on pipeline service or at shut down period? thanks to all helps
  4. redha123

    Intelligent pipeline pigging cost !

    Hi did you performed in your plant an intelligent pipeline pigging? how much dose it cost? was it helpful ?
  5. redha123

    Fault isolation problems

    maybe the capacitf current (Ic) due to the earth fault is bigger than the protection rating current(Ir). the normal setting Ir>3xIc.
  6. redha123

    MV Cable calculation

    the classical case of a feeder MV cable for an impedance Z at L distance. actually i want to make a program that calculate and i hope enrich it step by step. thaks
  7. redha123

    MV Cable calculation

    It's incredible, i can't find any goo document to perform a MV cable section, so if an angel read this ...HELP. Thanks
  8. redha123

    3 pole or 4 pole breakers

    In the case of unbalanced system the neutral is not neutral ..!
  9. redha123

    start up current

    An induction motor has form 5 to 7 time power at starting than in nominal running. you have a motor: P=110kW -> S=138 KVA at nominal running. when starting : S=(5to7)x 138 = 690 to 966 KVA needed !it but yoy have just a generator about 480 KW-> 600 KVA. i thing you need to change the starting...
  10. redha123

    motor starting simulation

    HI You can test the two software, by using a known exempel, try a simple circuit with one source and one self (if you want R+jX) but constant R and X. compare with your calculation note ! still use P.U .
  11. redha123

    Big motor starting

    There is a method not widely used : conecting capacitors during starting motor, this method is delicate because of overvoltage risk.
  12. redha123

    HV Cable calculation

    I have to feed Base Camp, power needed 4 MW, 5,5 KV (50Hz, the cable length is 6000 m. how (formula or the norme) must i choose the cable ?? what is the right steps ??? thanks.