For one way shear using the detailed method in ACI318, 'pw' is used in some of the equations which accounts for longitudinal tension steel, the simplified method for one way shear does not account for any steel.
We're working on a project in Flood Zone VE and are currently looking at the flood design loads on concrete shear walls below the DFE. We have a number of wall generally orientated perpendicular to each other distributed throughout the structure but with sufficient clearance to allow for the...
RAPT,
I know I'm based on the US where unbonded tendons is common practice, however, based on the OP's previous posts I assumed he was referring to bonded tendons and so the maximum tendons length I provided were based on PTIA's 'Practical Pretress Detailing' - are you recommending the values...
The maximum pour size is determined by site logistics how many concrete trucks the contractor can get to site before they need to stop. The maximum I've experienced is 1200m3 in a day
For tendon lengths, about 30m for a band beam, 40m for a slab tendon. If you use double live end tendons you...
Yes, I'm using the Wood-Armer method for twisting moments in the design strips, that's my default for all RAM models.
I will try setting the program designed rebar to user deinfed bars. I've never done that before, but can see how this could this could help.
Thanks Celt, you've been very helpful.
I'm using RAM Concept which can get a little funky sometimes when it comes to shear reinforcement. At the moment I'm using the simplified shear formula but I'm intend to work up a spreadsheet to use the detailed method so I can justify the larger shear capacity. I'm also not considering Vu >...
Thanks Celt,
My slab is 16" thick. I've ran some hand calculations to check the one way shear and it is required. The software is showing the shear reinforcement where you would expect it, and is consistent with my calculations.
You can't double count the shear reinforcement - is this stated...
I'm designing a transfer slab with no drop panels and I'm finding I need both one way shear and punching shear reinforcement which is something I never encountered before. I normally provide drop panels to avoid needing punching shear reinforcement altogether and so I just have one way/beam...
Where are the partition loads applied? 18kN/m is significant, I hope its supported on the beams.
A sketch showing the framing arrangement and application of loads would be helpful
Aside from the obvious structural issues identified above, I've never seen a balcony slab set higher than the internal slab. I hope the architect has a tried and tested weatherproofing/waterproofing detail to handle this situation.
AISC Design Guide 1 recommends a limit of about 24in to prevent issues with warping due to the thickness of the plate when fabricated, assuming a 1/4in. plate.