Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by mtngreen

  1. mtngreen

    floor construction of walk-in freezer

    Freezers require an underfloor heating system as explained above or the frost will heave the concrete. Either a radiant system (typically operates at 60F) or an underslab ventilation system, either forced or gravity.
  2. mtngreen

    Hot & Cold Well Design for Chiller

    Depends on chiller flow rate and process flow rates....need more info.
  3. mtngreen

    What is the lowest temperature with a ammonia refrigeration system?

    -60F is about as low as you can get.
  4. mtngreen

    install vsd on existing lead/lag chilled water system

    I would also plan on installing motorized isolation valves on the chillers that is isolate the chillers when not needed.
  5. mtngreen

    FDA & USDA required temperature for washdown

    I've seen between 140F and 180F depending on products being produced.
  6. mtngreen

    Anhydrous Ammonia Branch Line

    Suction line I presume. The orientation is usually off the top or 45 deg. but really depends on where in the system the connection is going.
  7. mtngreen

    unit heater control - 3way or run wild?

    In addition, if the system pumps are running off VFD's the lack of control valves on the UH's can provide the minimum flow requirements of the pumps.
  8. mtngreen

    Ammonia Refrigeration

    Oil cooling for the compressor.
  9. mtngreen

    Salami Drying

    I agree with MechEngNPE. Having a qualified engineer with experience in food/meat processing HVAC systems will bring a lot to the table.
  10. mtngreen

    CFMS vs Tons

    If you are using standard AC units forget the ACH calculation and base the CFM on the load calc. The ACH calc has nothing to due with the heat gain into and within the room.
  11. mtngreen

    Insulating Compressed Air Lines

    Use one of these for water removal....cheap and simple. http://www.drain-all.com/
  12. mtngreen

    Tag numbers for manual valves?

    I've designed ammonia refrigeration systems that have valve tags...one thought I've been kicking around is the use of RFID tags to store the information on the valve itself in addition to the valve number. Anyone doing this?
  13. mtngreen

    Air compressor auto drain help?

    check this out: http://www.drain-all.com/ I've used these a number of times with sucess.
  14. mtngreen

    Outside Air Intake Snow Melting

    Check out: http://www.mistop.com/snostop.html
  15. mtngreen

    Air conditioners in a basement.

    Couple questions: Is the space ventilated? Whats above the basement area? First reaction is that this is a bad idea for a number of reasons.