Here...try this link:
https://www.vertiv.com/49f28b/globalassets/products/critical-power/uninterruptible-power-supplies-ups/liebert-nxl-operation-and-maintenance-manual_00.pdf
Page 57...
Mike
Mike
Old motor nameplates, I believe, were Div 1 capable (going by memory, so double check me on that). However, as described previously, check w/ your process engineer to ensure Group D is still applicable. Often-times in the plant where I worked, process chemicals were changed routinely and motor...
Hi cuky...
Noted. However, I think the OP was referring to LV breakers. While the standard is old, the testing X/Rs haven't changed to my knowledge.
Mike
Mike
Often-times if you ask, the manufacturer's have the harmonic spectrum for their drives. Can you model the system using SKM, Easypower, etc. and see what the overall harmonic spectrum is? That should get you fairly close. Also, IEEE 519, IMHO, is often misapplied. Furthermore, I have seen current...
Incidentally,
We were reading unbalanced currents on both the line and load sides of the VFD. That can't be good...
(I'm not sure of the % of unbalance. I'll know more in a couple of weeks...the monitoring period)
Mike
All,
I have a motor (of which I do not have a nameplate to verify HP rating), which belongs to a process. The process owner wants to purchase a new motor, but with no nameplate, we are unsure of what to purchase (a new motor was purchased at one point and it turned out to be wrong). The motor...