You'll have to do your due diligence and check the frame sizes with the corresponding motor group. Also, be careful with AIT and any VFD applications as it pertains to motor inverter duty capability.
Mike
PS for example, you may have a motor spec that gives a T3C temperature code for a sine...
Maybe this will help: IEEE Std C62.22TM-2009
Mike
PS Found this paper as well: https://www.sciencedirect.com/science/article/pii/S0378779621005642#:~:text=Line%20surge%20arresters%20are%20installed,to%20a%20poor%20soil%20conductivity.
Assuming you have a MV or HV circuit breaker w/ no "brains", the relay is the brains. So, there will be a slight delay between relay sensing, and the relay issuing a trip command. So it would actually be longer than 2 sec, unless you included the opening time of the breaker.
Mike
There are usually interlocks between a VFD, load side disconnect and the VFD itself (I've never used a starter on the load side of a VFD, but have installed disconnects on the load side of a VFD for local isolation). Drives don't like switching actions on the load side of their terminals while a...