  1. mmt019

    Locating Oil type transsformers inside building

    NOt sure what you mean by "globally". I would be in an industrial setting in an electrical room in USA.
  2. mmt019

    Locating Oil type transsformers inside building

    Is there a problem with locating a 7.5 MVA oil transformer inside a building? I would use FR3 oil and still build a containment area for it.
  3. mmt019

    Is cable properly protected or not?

    I need some opinion. Attached is the image of the one line which shows a 3750 kVA transformer (XFMR-MSC-1). As it is a supervised location so as per NEC table 450.3(A), the transformer secondary protection is not required if the rating of transformer primary fuse is maximum 250%. However the...
  4. mmt019

    De-rating Required for Cables for Frequencies other than 60 Hz According to NEC

    Is there anything in the NEC about de-rating cables due to frequencies other than 60 Hz. I am working with 100 Hz.
  5. mmt019

    Replacement rheostat for synchronous motors

    I have six M-G sets from the 1940's where the synchronous motor utilizes a motor operated rheostat. The field voltage is 250VDC. The rheostats are in old and in need of replacement (or repair). I have not been able to locate a manufacturer for rheostats. I have tried Ohmite, Cutler-Hammer...
  6. mmt019

    Synchronous Machines

    Does anyone happen to know of the best reference for theory on synchronous machines and the theory behind the various field exciter equipment options for these machines? There is alot of reference material out there on the subject but is there one that is preferred among the EEs out there?
  7. mmt019

    NETA MTS-2011 Microhm Contact Resistance Measurement

    NETA MTS-2011, Part 7.6.1.1, Section 3.2.3 indicates that the contact resistance, in this case on a molded case circuit breaker, that in absence of manufacturer's data, the standard suggests to investigate the problem if a value deviates from adjacent poles or similar breakers by more than 50%...
  8. mmt019

    Megger test results

    The readings appear to be acceptable in accordance with NETA ATS-2009. I'll reiterate what others are saying: Check with the manufacturer, verify that the 'B' phase arrestor is the same as the others, retest.
  9. mmt019

    Odd Phase to Ground Readings on Delta Transformer

    Just a follow up to my problem, the ground fault was found to be a tubular heater (strip heater) for a synchronous motor and it was connected on 'B' and 'C' phase. Thanks for your posts!
  10. mmt019

    power system protection video

    Give this website a shot. I took a course in person with the instructor and he is very knowledgeable with this subject. Copy and paste on the link below. http://www.brainfiller.com/stores/productlist.aspx?CatId=7 Good luck!!
  11. mmt019

    Odd Phase to Ground Readings on Delta Transformer

    Our electricians record monthly readings and for years, it typically has read normal, 277V. So a change of some sort has taken place. A classic ground fault reading should have caused the faulted phase to drop to a much lower voltage. In this case, 'c' phase increased significantly.
  12. mmt019

    Odd Phase to Ground Readings on Delta Transformer

    I have a switchgear lineup that is fed by a 6MVA 6900/480V oil transformer, Delta configuration on both sides. On the switchgear, I am getting unexplainable V(line-ground) readings as follows: Va-g=215V, Vb-g=225V, and Vc-g=390V. Normal readings would be Vline-grd=277V. Phase to Phase...
  13. mmt019

    14 % Harmonic Distortion at residential customer

    Sounds like your best option is to move or become an Amish farmer. On a more serious note, turn off all of your feeder circuits on your panelboard and then see what your getting. This may clue you in to where the problem may be occurring. If your THD problem disappears with all your feeder...
  14. mmt019

    5A CT secondary

    What is the manufacturer and Cat # of the CT?