  1. MisterBill

    drop panel length in 2-way flat slab

    A23.3 clause 13.2.4 gives a maximum limit of Xd = Ln/4 ... Xd/Ln < 1/4 When you design start with Xd/Ln = 1/6 and if needed work there way up to 1/4
  2. MisterBill

    Loose Lintel Angle Design

    Equal leg angles are scaled up by a factor of 1.56 for deflection provided you are using the Ixx They should be designed for the full height of brick above. Deflection will govern L/480 (see s304.1 masonry code Canada). Even if you have a control joint on one side only arching is ineffective...
  3. MisterBill

    roof ridge beam support

    I think the single dashed line in the loft space represents where the ceiling goes from sloped to flat. The architect did not fully clarify this but I think a lot of the ceiling is flat. The dormer on the left shows single dashed lines and there is a single dashed line where the stair is. I...
  4. MisterBill

    Steel framing design for elevator guide rail forces and reations

    I am no expert on elevators but I think the rails are designed to span floor to floor. Generally the rail is supported by an HSS section because the rail won't have the strength to take the imposed loads. The HSS section is welded to embedment plates installed in the shear wall or to an...
  5. MisterBill

    Reinforced Masonry - Partial Grout

    Here is a link to some design calculation. There are alot of examples on this youtube site (Struct2009). They deal with both Masonry/Concrete design and Canadian Codes. http://www.youtube.com/watch?v=8RliuJNL8Ys Regards,
  6. MisterBill

    Car park deck loads

    Live Load is 2.4 kPa (Car Traffic Only) For Dead Load you need the slab thickness and topping.
  7. MisterBill

    Steel lintels for 10&quot; CMU

    For Steel Lintels in existing 240 masonry wall. Install angles toe to toe (weld tie plates to the flange and/or bolt through) |_ _| 102x102x9.5; Span<1200mm |_ _| 152x102x13 LLV; Span<3600mm For Steel Lintels in new 240 masonry block walls install angles back to back and stitch weld _||_...
  8. MisterBill

    Pre-manufactured Metal Building Foundation Design

    The adjacent/Flanking foundation walls alongside the pier may provide additional dead load. So the wall footings, soil and selfweight of wall all contributed to the dead load too. But if it is an isolated interior pier then you may have to lower the underside of footing elevation to get the...