Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by mihmb

  1. mihmb

    Basement wall Design calculation

    TDI Engineer, What methodology do you use to check seismic soil loads against a wall? The reason I ask is because I recently had a to perform such an analysis for an existing cantilever retaining wall. I was lucky enough that I could use some very conservative loads and the wall was still...
  2. mihmb

    Basement wall Design calculation

    TDI, what is the basis for "On retaining walls greater than 15' a seismic pressure should also be considered in high seismic zone." The 15' is new to me. Can you please clarify?
  3. mihmb

    Basement wall Design calculation

    Jae & MS, When the floor joists are X braced together, this transfers the load to the diaphragm. I believe that the X bracing I am referring to serves the same purpose as the bocking you are referring to. Please correct me/explian if I am missing something. I personally have never seen the...
  4. mihmb

    weld designation on back to back channels

    If you want these channels to split the loads, you need to "unload" the existing channel before installing the new channel. Otherwise, the load the existing beam is already seeing will always be there and the new beam will only take 1/2 of any load applied after the modification. I would...
  5. mihmb

    Basement wall Design calculation

    The wall that does not see the bearing load from the floor joists still has a joist setting on it along the entire lenght (sets parallel to the wall). The plywood subfloor is attached to this joist, this acts to resist the load as it is essentially a large diaphram. Additionally, floor joist...
  6. mihmb

    Basement wall Design calculation

    For a single story basement. General assumption is the wall spans vertically with end conditions being pinned at the top and the bottom. One could assume bottom to be fixed, but proper detailing of this connection would need to be done. Depeding on type of construction this may or may not be...
  7. mihmb

    Seismic Engineering Continuing Education

    I am looking for continuing education oppertunities to development in the structural seismic/earthquate field. I have done some interent searches and everything thing I see is very high level. I want to dig into details and a good solid understanding. Any suggestion? Thanks in advance!
  8. mihmb

    Who provides leveling nuts or shims?

    I would call both of them up and say. "I am sure if I look hard enough I am sure I can find somewhere that you did not meet project specs... Or can I see your documentation proving that you provided the exact ASTM/ACI spec on XXX (you choose, conc mix, w/c ratio, anchor bolt)." Or ask them if...
  9. mihmb

    Did not receive the raise i wanted, now what?

    Be patient. What you are experiencing is not the exception, but the norm. I have two examples for you. Myself, I graduated in 2006. 1st year raise = 4.5%, 2nd year raise = 9 % (I was told it was because I did such a great job that year, but later came to find out it was cause they hired...
  10. mihmb

    please help me size a weld

    You do not need the gussets. Weld the HSS all around to the column. DONE!
  11. mihmb

    Upcoming review, need advice...

    I am looking for advice on how to approach my supervisor for a raise. Our yearly review is coming up shortly. The company I work for is great and I really like it here, however there are a few things that bother me. For one, when I go in for my review my supervisor has a number set for my raise...