Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by KZ001

  1. KZ001

    stratification question

    It's a office building
  2. KZ001

    stratification question

    Hi, Does anyone know if comfort is a requirement in the latrines and shower areas? Can you allow some stratification?
  3. KZ001

    Calculation of converging bullhead tee

    Thank you everyone! kacarrol, I have the same document but the source is unknown and I am not sure if I reliable. Thanks again!
  4. KZ001

    Calculation of converging bullhead tee

    The pressure loss for a converging bullhead tee is not listed in the SMACNA "HVAC Systems Duct Design" or the ASHRAE Fundamentals.
  5. KZ001

    Calculation of converging bullhead tee

    Hi, How do I calculate the pressure loss of a converging bullhead tee in a return duct system. The tee has dimensions 23"x23" for the main duct and the branch. Thank you!
  6. KZ001

    Plenum return pressure drop (HVAC)

    HerrKaLeun, Thank you for the question! I have a supply duct in the plenum, not sure if there would be any electrical conduits. Most of the plenum height is 2’, there is only one room above which the plenum height is 1’.
  7. KZ001

    Plenum return pressure drop (HVAC)

    Drazen, When I calculate the PD through the plenum with concrete walls, can I use the same pressure loss chart for metal duct? Where do I get a chart for concrete wall duct?
  8. KZ001

    HVAC question

    Outdoor air is not acceptable, there is a coal plant close to the building.
  9. KZ001

    Plenum return pressure drop (HVAC)

    Hi, I would like to calculate the return air pressure drop through a plenum between the first and second floor of a building. The building 1st and 2nd floors shear common plenum return. Do I have to take into account the pressure drop of every single return grill on the ceiling of the first...
  10. KZ001

    HVAC question

    Thank you everyone for your help! I am sorry I should’ve clarified that I am using WSHP to condition the room. The WSHP is connected to a closed loop cooling system. The cooling system is designed to carry heat away from the electrical equipment. That energy can be utilized to heat the space...
  11. KZ001

    HVAC question

    The design temperatures are 72F and 76F for heating and cooling respectively respectively. Not familiar with heat rejection system. There is a cooling system in the equipment rooms that utilizes a water as cooling fluid.
  12. KZ001

    HVAC question

    Hi, I am designing a HVAC system for an equipment room that houses a large electrical apparatus. The load in the room can vary from 10,000Btu/h to 85000Btu/h. The room area is 1345ft^2. Should I use CAV or VAV box?
  13. KZ001

    HVAC Climatic Design

    HerrKaLeun and MintJulep Thank you!
  14. KZ001

    HVAC Climatic Design

    Thank you willard3! I was not sure if 1% means that the design temperature has been exceeded only 1% of the time during the year or the design temperature occurs only 1% of the time during the year. However, I think that my first assumption is correct. Please let me know if I am wrong. Thanks!
  15. KZ001

    HVAC Climatic Design

    Can someone define “coincident 1% outdoor ambient dry-bulb temperature”? Thank you!