Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by jghrist

  1. jghrist

    Install Difference Voltage Rating 24 kV to 13,8 kV

    The control voltage will be wrong. Depending on the make/model, you may be able to add a VT to correct.
  2. jghrist

    Double Ellipse Galloping

    Best reference that I've found is RUS BULLETIN 1724E-200 DESIGN MANUAL FOR HIGH VOLTAGE TRANSMISSION LINES, Section 6
  3. jghrist

    Code Question: Residential Elec Equipment Mfg Suggests Running 120v Conductors In Conduit Without Neutral

    I'm confused. Where are the circuit conductors connected to the load? At the panelboard, at the transfer switch, or both? Can you provide a one-line showing the circuits? Your other post said that the panelboard provided o/c protection when connected to the utility and the transfer switch...
  4. jghrist

    Help calculating voltage drop through storm water

    There are many choices for splicing 15 kV cables. All capable of being under water. Being above ground pretty much requires an enclosure and splices like elbow connectors that do not have be in-line. I would rule out hand taping.
  5. jghrist

    Current division for fault on high side of substation

    I think the missing 36A is because phase angles are not shown and the different currents do not have the same angles. The diagram would be clearer if they showed the currents flowing into and out of the structure grounds. Neglecting phase angle errors, the current flowing from the...
  6. jghrist

    Help calculating voltage drop through storm water

    I also would worry more about the secondary. Primary elbow connectors are submersible and shouldn't create a fault when flooded. You could use submersible connectors on the secondary also. This doesn't prevent faults at flooded building service entrances, which would be a problem even if the...
  7. jghrist

    Earthing of neutral point of power transformer

    Your use of the term "earthed" instead of "grounded" makes me think that you are from the IEC world (UK, Europe, SA, etc.) not North America. The MV distribution systems in NA are very different than those in the IEC world. NA utilities have a lot of single phase transformers and laterals that...
  8. jghrist

    Switching a transformer on and off with something to reduce the inrush current

    What controls the output voltage of the solar power? If you lower the voltage it will reduce the inrush.
  9. jghrist

    480V ungrounded Delta

    Why not connect to the 13.8 kV with a Dyn transformer that would provide the grounding of the 480 V system?
  10. jghrist

    Soil electrical resistivity measurements for a wind turbine location

    A lot depends on how variable the soil resistivity is. Of course, that's hard to tell without making several measurements. Variation with depth can only be determined with long traverses. It also depends on critical the resistivity is. I'm not familiar with grounding wind turbines, but...
  11. jghrist

    Soil electrical resistivity measurements for a wind turbine location

    I would suggest 2 cross measurements for each wind turbine. The maximum probe spacings depend on the diagonal dimension of the turbine ground grid. See IEEE std 81, Guide for Measuring Earth Resistivity, Ground Impedance, and Earth Surface Potentials of a Grounding System, for guidance.
  12. jghrist

    Incoming device as Disconnector Switch / Isolator

    I think the Mar 23, 2013 date is when you set up your Eng-tips account.
  13. jghrist

    Incoming device as Disconnector Switch / Isolator

    | don't think it is either an IEC or ANSI symbol. Looks more like a horn gap switch symbol, but that would not provide the protection needed.
  14. jghrist

    87T multi-terminal application

    You need a three terminal 87T, with the third terminal connected to CTs on the 4.16 kV side of TR-2k.
  15. jghrist

    SEL 651 indicator light showing open when closed.

    It's either a programming issue or you are connecting a "b" contact to the relay input instead of an "a" contact.

Part and Inventory Search