Recent content by HYDL

  1. HYDL

    3-pole ATS and breaker trip during transfer

    We recently installed a new Asco closed transition ATS to feed a new data center at a hospital. To test the system, the electrician shut off the utility breaker feeding the transfer switch and the generator started up and the ATS transferred to emergency power. After the test was over, the...
  2. HYDL

    Mysterious Voltage Potential

    I think what they may have going on is a high soil resistivity problem. Do you have any experience with a high soil resistivity and what occurs. I have the lightning protection folks checking that the bonding of the electrodes is complete.
  3. HYDL

    Mysterious Voltage Potential

    Sorry if the info seems irrelevant....I tried to post what the contractor in the field reported to me. We did the lighting and power system engineering design for the building. The contractor is now installing what we designed....ie lighting, power, special systems. This voltage issue came up...
  4. HYDL

    Mysterious Voltage Potential

    We have a project at Yellowstone National Park and the contactor is experiencing a voltage potential issue. It started with a 5 volt potential between metal steps, in contact with the ground and the various job trailers. They turned the power off at the meter pedestal, which disconnected all the...
  5. HYDL

    Equipment Ground currents

    This is a 1200 amp emergency feeder at a Hospital. EGC has 1.9 to 4.8 amps and max of 12 amps of leakage current.
  6. HYDL

    Equipment Ground currents

    Is there a standard that dictates how much equipment ground current is too much? Certainly, the ideal is zero, but what would be considered an acceptable level?
  7. HYDL

    Grounding Electrode sizing

    I am looking for information on how the NEC 250.66 table was derived for sizing the grounding electrode.
  8. HYDL

    Bussman Point by Point AIC Calcs

    Any more thoughts on the derivation of the point-by-point formulas?
  9. HYDL

    Motor Whining

    Thanks for all the input. Very helpful.
  10. HYDL

    Motor Whining

    I am trying to learn what I can about Motor Whining. We have a cooling tower motor at our building that has a significant Whine. It is served by a VFD and I'm thinking that this may be the reason. Anyone have any input in this regard?
  11. HYDL

    Bussman Point by Point AIC Calcs

    Thanks for responding. I understand the M being a percentage of available fault. What I'm trying to do is disect these formulas to determine how they were derived. All items in the f formula I can account for, but I'm not sure why they add 1 to the f and then take the inverse.
  12. HYDL

    Bussman Point by Point AIC Calcs

    I've been evaluating the Point by Point method of AIC calcs that is in the Bussman Fuse book and also indicate in other literature. They have calculation for an f factor and an M factor. I'm trying to figure out where they come up with the M factor (the multiplying factor) 1/1+f.
  13. HYDL

    Wye Wye vs Delta Wye Transformers

    Thanks all for the good information. I couldn't think of any reason to go Wye Wye. The system will not be paralleled with the utility. I'm finding out that they actually want this to be a portable setup on a trailer or two.
  14. HYDL

    Wye Wye vs Delta Wye Transformers

    I 3 paralled Generators to power an Industrial System Wye System. This is a prime power application. The Generators will serve a Transformer that is 480v - 4160v Wye. The plant is mostly motor loads and will likely have some harmonics due to VFDs. I'm wondering if I should go with a Delta at...
  15. HYDL

    Evaluating Harmonics

    I've been monitoring Harmonics at a 911 call center. They have two 12.5 KVA, 1-phase UPS at 240 volt. The 208 volt system has a boost transformer for each for the 240 volt. I've review the IEEE 519-1992 document. 3.5% is the highest THD that I've measure at the line side of the system. So...