@ALphaSpace if you've allowed for the moment and the axial load and the cantilever column effective length...why are you using a 200x16 SHS that is ~2.5x the strength it needs to be?
Surely you could adopt a more economic section
Considering that you have a column either side + welded beam and...
Choras, it looks to me that the column is used to support the 2 flights of stairs and has beams welded off to take the load
These will prevent buckling in that direction
In the other direction there is no restraint therefore the design has two 'restraint beams' at each level - these are the ones...
The only thing that comes to mind is that this is probably appropriate for a UDL but may not be appropriate for a point load
Wind uplift on a metal deck - sure
Footfall at the end of a cantilever? The local effects of the point load may cause a different failure mode to govern
This insight...
Braced frame could be channels with their webs against the block and bolted into it
Doubt you'll get a (reasonble) moment frame to be stiff enough to compare to a wall
Could look at building new pilasters at the ends of your openings to frame them out and create boundary elements for the wall...
I'm not aware of a specific reference. I don't think one is needed though: working through this rationally is what engineers are paid for
I work in a high seismicity country so am familiar with the intricacies but not US specific stuff
Issue 1 - providing appropriate gravity support to your new...
I went to an S&T presentation a few years back that showed different but very similar testing with the same results
I recall that the explanation is that the narrow shape of the compressive element constrained the compression shape from fanning out and limited the transverse tension strain
This...
Are the walls underneath the slab or above it?
You have to be very careful with mixing and matching raft/piles and walls/strip footings
I have been dealing with a damaged house that has a basement with this system...the walls have settled far more than the piled foundations and there is now a...
No I don't agree with that. The point is to ensure that some steel is fully developed...doubling the steel and putting in shitty development length on both doesn't meet this requirement
Also, I suspect that the development length required is more than 230mm?
You have 12db PLUS a cog (which I'm...
This is my guess as well, though I'm dubious of this detailing in practice
That said, I've seen similar (and worse) detailing here in NZ and haven't observed issues yet...
@
Your logic is inconsistent.
Currently, it sounds like you're wanting to avoid designing the concrete as a column but also want to rely on it as a structural element - you can't have your cake and eat it too
There are two ways that the concrete encasement can stiffen the W steel beam
1/ By...
Well that detail already shows one of the difficulties with this theoretical detail - you still have a moment capacity at the base, it's just that the lever arm has reduced to half the width of the wall at the critical point. It's not like it has zero moment capacity, it just has a lot less. And...