  1. godel123

    SSV closing time

    thanks for all
  2. godel123

    protection curve but only a point (overcurent 51)

    how to "choose" the seting values to protect a motor, i mean is there a genral considerations or we have to make calculations? exemple of a motor : 50 Kw, 400 V.
  3. godel123

    protection curve but only a point (overcurent 51)

    hi overcurrent (51) protection. When we see 100 A 0.3 s. so why we talk about curve, but there is only a point
  4. godel123

    SSV closing time

    there is also a maximum velocity of the expansion of the spring when closing the valve, which is insured by limiting device in the control panel
  5. godel123

    SSV closing time

    Thank you for your answers. as we only have values ​​without Reference to any standard , i'm looking for a document that gives an explanation.
  6. godel123

    SSV closing time

    it's a hydraulic actuator the distance between the Christmas Tree and the control-panel is 50 meters
  7. godel123

    SSV closing time

    ssv : surface safety valve 15 s : is there a standard or is it a best practice or a company specification ?
  8. godel123

    SSV closing time

    hi What is the maximum time expected for SSV to close (by de-energize the hydraulic control of actuator) ?
  9. godel123

    CT magnetization

    indeed , passing a direct current will magnetize the CT.
  10. godel123

    power cable for motor with protection cable

    the earthing system (localy buried on field near motors) is not enough for desipation of fault?
  11. godel123

    power cable for motor with protection cable

    it's LV , 3phase +ground, the cable is armored the earthing system is every where aroud the motor location. i thought the use of the metallic armoris enough to use a torus.
  12. godel123

    CT magnetization

    if you inject DC==> no induction
  13. godel123

    power cable for motor with protection cable

    hi to feed a motor when should we use (exemple) 4g70 sqmm instead of 3x70?
  14. godel123

    standard about Air Tank Accumulators required for SDV or BDV

    hi is there a standard talking about the necessity to add an air tank accumulator for BDV or SDV?