The AVR is a BRUSH Static Thyristor Automatic Voltage Regulator (STAVR) and was manufactured by them to provide excitation generally to salient pole generators fitted with a permanent magnet generator.
1. The Voltage Setting Potentiomeeter is the +/- 10% voltage adjustment of the AVR, the hand...
If you open the Component Editor (top left icon) in the Menu Bar, you will be able to identify and delete the component by right clicking it, this will open the sub menu allowing you to then destroy the component.
Depending on the version of SKM you have you may also find unused components by...
The fact that you have not destroyed the component means the original name still exists as the component is still in the model.
I believe you will have to either use a new name or destroy the original component in the Base scenario and start again with a new component using the old name.
I believe there is no merit in carrying out a PI test on the 480V LV winding, I am suprised you managed to get a PI as high as 2. I only carry out PI tests on 6.6kV and above using a 5kV DC megger. I would recommend that you energise the transformer as the insulation resistances you have...
It sounds like the voltage droop characteristic of the AVR is incorrect. The AVR droop setting should provide a falling voltage characteristic for increasing lagging reactive power. If the droop CT is either in the wrong phase or wrong polarity the AVR output will increase instead of decrease...
Has anybody any practical experience of carrying out DD testing on XLPE (11kV) cables. I understand the principles of the test but would be interested to here from others who have actually applied the test in the field and may be able to provide some indication of its effectiveness.
I've been using SKM Power Tools for a few years now, I use it for short circuit studies, load flow, protection grading and also dynamic studies on rotating machines. Never any problems with bugs etc and relatively simple to use, I would recommend it.
Under excitation or even a loss of excitation does not allways lead to a loss of synchronism, for instance if the motor is lightly loaded. An under excitation relay can be used but there is allways a risk of spurious tripping during motor supply voltage dips. Most modern protection systems for...