Recent content by ffont

  1. ffont

    Replacing a Delta Distribution transformer feeding an existing Delta load by a Y-Y transformer

    Our distribution grid is a Y-Y multigrounded system, so we plan to replace the few existing and old delta transformers feeding delta loads with standard Grounded Y-Y distribution transformers (500kVA to 3000kVA), with the star points solidly grounded on both side; a three wire circuit will feed...
  2. ffont

    Back Feeding a single phase pole top distribution transformer

    We have a 24940GRDY system, (14.4kV L-G) and in order to avoid installing a MV single phase metering unit to feed a small 37.5kVA single phaseload requiring 2400V, we plan to use some units we have in stock, ie a step down 100kVA 14,4kV-120/240, and connect its 240V to the 240V LV of a 75kVA...
  3. ffont

    Unbalanced load in a 5 MVA Delta-Wye transformer (24940V-4160V)

    Our main distribution system is multigrounded Y ( 24940GrdY/14400V) but to feed our older 4160GrdY/2400V downtown system we typically use some 5MVA Delta-Wye transformers (24940D-4160Y). The 4160V system is typically well balanced. However, we need to remove some of the loads from it, and...
  4. ffont

    Replacing a 1500kVA 3 phase Delta

    For mgtrp.... thanks! I can see the voltage collapse in the LV ground faulted phase and the corresponding shift of the neutral in the primary. I taught there would be some zero sequence flowing in the ground, but with no voltage there can be no current. It makes sense. But then, can you help...
  5. ffont

    Replacing a 1500kVA 3 phase Delta

    Stevenal and mgtrp, will there really be no zero sequence currents flowing in the LV grounded neutral? The Primary will be an ungrounded wye, but the secondary will be solidly grounded. With no zero sequence current, I am increasingly worried that this may lead to ferroresonnance if one of the...
  6. ffont

    Replacing a 1500kVA 3 phase Delta

    An industrial customer is currently fed via a 2000kVA 13860V delta-600 GrdY 347V. The medium term plan is to replace the 13860V system by a 24940GrdY system, and install a new 2500kVA transformer connected GrdY-GrdY What would be the drawbacks to remove the present transformer (delta primary)...
  7. ffont

    Impedance of 3 phase bank (3 single phase GrdY-GrdY)

    Bill, thanks for clearing this up....
  8. ffont

    Impedance of 3 phase bank (3 single phase GrdY-GrdY)

    cuky, I see indications showing the %Iz of the 300kVA bank as being 3 times the % Iz of the individual single phase. This is really not the case..... eg if all 3 single phase units had a 1.6% IZ (on a 100kVA base), then the 3 ph bank has a 1.6% IZ as well (on a 300kVA base).
  9. ffont

    Impedance of 3 phase bank (3 single phase GrdY-GrdY)

    Bill, David and Jghrist, thanks for the answers, we did indeed suggest to the consultant to use the lowest %Iz on a 300kVA base as the worst case scenario for a 3 ph short circuit... but he insisted! go figure! With regards to the fact that the Nameplate %Iz is obtained using the LV winding...
  10. ffont

    Impedance of 3 phase bank (3 single phase GrdY-GrdY)

    I have a three phase pole mounted bank made out of 3 single phase transformers 100kVA 12470GrdY/7200-120/240V. The %Iz of each transformer is respectively 1.9%, 1.8% and 1.6% on the 100kVA base. The transformers are connected as a 12470GrdY-208GrdY bank (The 2 LV windings of each single phase...
  11. ffont

    Three single phase pole tops in a 3 Ph bank

    These transformers are wound core, shell type ie the HV and LV windings are wound concentrically on the same bobbin. In this case the HV winding is sandwiched between the 2 - 120V windings. This is a very common design practice to obtain a low % Iz for these lower distribution kVA sizes. The...
  12. ffont

    Three single phase pole tops in a 3 Ph bank

    There is an application for a GrdY-GrdY bank using 3 single phase transformers 14.4kV-120/240 into a 24.9kVGrdY-208GrdY bank. 2 of the units are 100kVA, with an 1.8% Iz and both will have their 120V LV winding paralleled; the third transformer is a 200kVA, same voltages, 2.2% Iz but only 1 of...
  13. ffont

    Y-Y transformer bank with LV grounding resistor

    David Beach Thanks for the answer! the medium voltage system feeding the bank of 3 - 167kVA is a solidly multigrounded 24.9kV. So for this appliaction (ie a NGR in the LV) the H0 must be solidly grounded (as Waross indicates, tied to the system ground). The LV X0 must then be an insulated...
  14. ffont

    Y-Y transformer bank with LV grounding resistor

    We are looking at installing a three phase transformer bank made out of 3 single phase oil filled transformers rated 167kVA each, to feed an small industrial load. The HV is a 4 wire system 24940GrdY14400V The LV neutral will be connected to ground via an NGR If we choose a Y-Y connection, I...
  15. ffont

    Three Phase distribution transformer banks

    Bill, Absolutely correct... and the same goes for Voltage Regulation as it is a function of %Ir and %Ix There are many good articles on paralleling, but do you (or anyone) have any article that develops single phase banking in a three phase bank, specifically for GrdY application? The idea is...