Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by davrom

  1. davrom

    Short Circuits Calcs w/ Transformer Taps

    Aferguson, It is actualy the "MVA method" you referenced the "proportional units (pu) method" or the "common base power (MVA) method"?
  2. davrom

    Short Circuits Calcs w/ Transformer Taps

    musicguy1800, no offense was intended; I appologize if it sounded like that. It is only that you had a correct intuition (from my point of view). To Aferguson: I think your actual question is: "What is wrong with my equations when I consider the voltage taps?". Indeed, performing the...
  3. davrom

    Short Circuits Calcs w/ Transformer Taps

    Sorry for this late post, but I have had a long time reading and studying the info and formulae given by various members and trying to match them with the shc theory that I know (which I have learned at school). I come from a diferent school which sometimes (manytimes) has different approaches...
  4. davrom

    Voltage drop and short circuit

    I agree to jghrist. The voltage drops do not affect directly the shc current value. Basically and very much simplifying, the short-circuit reduces to a circuit formed by an equivalent impedance connected to the source (it is a "short" circuit). The shc current is basically I=U/z. The...
  5. davrom

    IEC Short circuit ratings for the Circuit Breakers

    To Voo: 1. A star to your post. Real thanks for info given upon the Icu and Ics currents. I knew the test sequences of each current (qualitative conditions) and the capability of CB to carry, resp. not to carry its rated current (quantitative conditions), but I couldn't understood the physical...
  6. davrom

    IEC Short circuit ratings for the Circuit Breakers

    Correction to my previous message: At note 6 please read "based on notes 4 and 5 ...".
  7. davrom

    IEC Short circuit ratings for the Circuit Breakers

    Hi uno. A. Please forget my first message. B. Sorry for this delayed response. My attempt to understand the differences between the three currents took me more than 1-2 days that I expected. I have been checking for and thinking to the three currents over and over again. I have come to some...
  8. davrom

    IEC Short circuit ratings for the Circuit Breakers

    Please excusse my English. Can you re-phrase the sentence "which in turn determine the short-circuit rating of the switchgear for 1sec/3sec (i.e. 40kA for 1 second)"? I don't understand. Thank you. For Icw (selection of CB based on the shc current value at time 1 second): No. The...
  9. davrom

    What is the r.m.s. value of a current?

    Thank you for your replies. I still have reserves for "wutz" (due to German influence - it would have been very easy to be used "what's"), but I am happy the matter has been solved out. Sorry for inadvertence.
  10. davrom

    What is the r.m.s. value of a current?

    busbar, what "FWIW" does mean? electricpete, what "Wutz" does mean? Is your irony strictly limited to my English or is extended over my person too? To the rest of the members: thank you all replying to my question. I have got the answer I have been looking for.
  11. davrom

    What is the r.m.s. value of a current?

    No, you don't! Thank you. It is indeed the "effective" value of a current.
  12. davrom

    What is the r.m.s. value of a current?

    I responded to a question of this forum (cable selection based on duty cycle) where I afirmed that the r.m.s. value is similar to the thermal equivalent current. I realized this may be a stupidity (in fact, I am pretty sure). I analyzed the problem and now I believe that the r.m.s. value of a...
  13. davrom

    Generator torque, internal angle and E0

    Thank you, jbartos. I am not an American teritorial and I cannot get the book you referenced, but thank you anyway. I have been thinking to the problem and the result is that I realized I made a mistake, resp. it is obviously that the torque is direct proportional with the load (I2 current); I...
  14. davrom

    Generator torque, internal angle and E0

    The question is refered to a 1P synchronous generator. It is known the output voltage U2, nominal power, revolution rpm, synchronous reactance Xs and pf of load (e.g 0.9 inductive). The rest of parameters are neglected/neglegible. 1. How can be determined the nominal internal angle teta, the...
  15. davrom

    Selecting power cable based on duty cycle

    Hi syssafety, It does not appear from your message if there is about a 3P (three-phase) or 1P (one-phase) system, and AC or DC system. This has impact on the number of conductors of the supply (feeding) cable, resp. 3 or 4 conductors for 3P systems (3 conductors for the 3 phases and 1 conductor...