NFPA 70E requires ventilation systems, forced or natural, to prevent buildup of explosive mixtures in battery rooms. A determination must be made for each battery area as to whether sufficient ventilation is being provided.
Reference your battery manufacturer for the hydrogren gas evolved, it...
I remember there was an IEEE Spectrum article on it awhile back, they seemed to be connected to both the French and Switz grids and ran somewhere inbetween 220 and 300 MW. but, this failure didn't have anything to do with where their power comes from, from the pictures it looked like a...
So I wonder if these nuclear physicists are a bit behind on cable testing practices. A comment like power failures are not that rare for a new $10 Billion accelerator seems odd to me!
It's possible the buffer is causing your issue, there isn't enough information from you to really make a decent conclusion, but at the get go, verify they haven't violated any devicenet wiring rules, ie: trunk length and terminating resistors on both ends for the Tx and Rx. You may need...
Maybe you can better define what electrical and comm are in this applicaton, but strictly speaking, if you are mixing conductors with differenet insulation ratings (ie: 300V and 600V) it's not permittted off the bat.
Also, if you dig into Article 800, it is also not permitted to mix...
Actually, it appears that none of the armored telephone cables are even listed for use in Cable Tray. Looks like there is little doubt I will have to install it in conduit.
I agree with using fiber too but that's another issue I asked about, but we still are required to run twisted pairs...
I am in the US, so hoping to get some thoughts from an NEC compliance perspective. We need to run a telephone cable and the only route is a 20kV cable tray with Type MC cable.
392.6 allows you to run Class 2 circuits in the same cable tray if the cables >600V are Type MC, however it appears...
Thanks for the link, however I already have looked through those and couldn't find what I'm looking for.
"Not sure how you ordered a replacement if you are not sure what you have..."
I am sure it is what we want since we use that model on the rest of our similar feeders for 67 protection...
I'm looking for the manual on an early type JBC Relay: Model 208A8458 G-2
The publication on the nameplate is 'GEK-36836', which is not on GE's website, and the folks at GE say doesn't exist, but that doesn't make sense because it's clearly engraved on the relay.
I am specifically looking for...
That is not true at all, and you shouldn't rely on anecdotal information. When a load has capacitance or inductance, the impedance will change with respect to frequency.
Not to hijack your thread, but I was looking at some 6 pulse rectifiers today. 2 of them were connected in parallel with the other, but the primaries were connected as shown in my attachment. This is supposedly a 12 pulse equivelant.
I do not see how you get a 30 degree shift from T1 to T2. Can...