Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by AusLee

  1. AusLee

    Lights flickering

    @3DDave thanks, you are right, and for the first link you sent I did contact SAL and asked them if the filter is in t he SDD 'dimmer' or if i just get the SFI downlights then they will include a filter as well: they said the lights will be flicker immune even on manual ON/OFF switching not...
  2. AusLee

    Lights flickering

    @stevenal thanks for your reply, there are a lot of apartments in the same building that are not experiencing any flickering. Also these are LED lights not incandescent: the incandescents back in the day used to have 'thermal inertia' to ride through frequency canhed, for LED: it all depends on...
  3. AusLee

    Lights flickering

    Hi, I got 2 other videos: Video 1 Video 2 This is high frequency and different in kind from the first flickers which appear to be voltage drop issue due to high impedance / loose connection. I have a feeling it is due to the controlled-load frequency that the supply authorty delivers in the...
  4. AusLee

    Lights flickering

    For the loose wiring termination, am I correct in understanding it this way: the loose connection is causing a high impedance contact with the power supply, therefore reducing the applied voltage. With the reduced voltage: the capacitors in the ballast do not have sufficient time to charge hence...
  5. AusLee

    Lights flickering

    Hi, What can be causing these lights to flicker? 1: https://www.dropbox.com/s/9wyc7vck7n7dkex/Defect%20%231%20-%20garden%20lights.MOV?dl=0 2: https://www.dropbox.com/s/cj6or3x1awmdhnu/Defect%20%232.A%20-%20garden%20lights.MOV?dl=0 3...
  6. AusLee

    Containment and termination of cables in harsh environment

    Hi, Can you please put a link to a whitepaper, forum or similar regarding the requirements for protecting electrical and control cabling in a fuel refinery? Something like: use X kind of heat shrink as the cable enters the conduit, then use cable glands type X as the cable enter the equipment...
  7. AusLee

    Looking for fast acting semiconductor fuses

    Hi, We have an expensive piece of equipment that can withstand only about 4,000,000 A²s let through energy. There is no circuit breaker fast enough to clear a fault that quick, so we would like to place a fused isolation switch right next to that device. The semi-conductor fuses should be...
  8. AusLee

    Calculating 3-phase fault from earth fault

    I got these formulas but wonderinig how to use them in HV: Z = impedance per phase ULN = phase to neutral voltage ULL = sqrt(3) x ULN 3-Phase fault: Ik = ULN / Z Earth Fault: Ik = ULN / (Z+Z0) and just for the record 2-phase fault: Ik = ULL / (2 x Z) which I think is easiest to understand...
  9. AusLee

    Calculating 3-phase fault from earth fault

    If anyone else is going to post, I appreciate that it is actually the formula how to calculate the 3 phase fault in HV from the earth fault thank you.
  10. AusLee

    Calculating 3-phase fault from earth fault

    @FreddyNurk You are correct, I am not designing for fault withstand capacity I am designing for grading. I know, the inclusion of the upstream impedance will reduce the fault level to its actual value not the theoretical maximum based on infinite upsteram bus. Yes I have your same assumption...
  11. AusLee

    Calculating 3-phase fault from earth fault

    I want to calculate the short circuit at my main switchboard. I have the transformer's data (2MVA, 6%) and I have the network upstream fault so I use: 1 / MVA system = 1 / MVA utility + 1 / MVA transformer I presume that's correct, right? Only one more thing: for the utility they gave me the...
  12. AusLee

    Connecting 240mm2 cable to 160A circuit breaker

    Thanks we decided to use Flexible Busbars.
  13. AusLee

    Connecting 240mm2 cable to 160A circuit breaker

    Hi, A 3 phase cable with 240 mm2 cross section for each of the phases is required to connect to a 160 A circuit breaker. The cable is too large (2.2 x the cross section of AWG 0000 (4/0)), and the terminals on the circuit breaker do not fit. What accessories would be a good 100% legit (not...
  14. AusLee

    Eathing continuiting of building structure

    Hi ScottyUK No we are not thre yet, RCD is required for many applications (AS 3000 section 2.6.1) but not for all applications and not for all concealed wiring. But I think the question is not only realted to concealed wiring, the question is whether or not the earthing of a metal part is a...
  15. AusLee

    Eathing continuiting of building structure

    Hi rtronics, yes precisely 5.4.6. the 0.5 ohms is for the bonding conductor itself not for the whole resistance of the bonding conductor + resistance to earth of the metal frame. the maximum resistance of the main earthing coductor connecting the earh bar in the main switchboard to the main...

Part and Inventory Search