  1. 22574

    PDC

    A core balance ground ct connection was used in O/L in a Motor, while residual ground CT connection was used for O/C at the secondary side of Transfomer going to the switchgear where the motor connected. My question is, can I coordinate the two relays? What is more sensitive during ground...
  2. 22574

    Generator tubular Busbar

    YES, Pls see specs below: Bus bar length per phase (6.260 mm) - Diameter = 1704 mm - Rated voltage = 17.5 KV - Conductor material = Hard Aluminum - Rated current = 4,170 A - Test Voltage = 38 KV - BIL = 95 KV - Number of...
  3. 22574

    Generator tubular Busbar

    Hi everyone, Can anyone direct me to supplier for a Generator Tubular Busbar? Thank you.
  4. 22574

    SR469 relay manual

    Does anyone have a copy of manual for SR469 relay?
  5. 22574

    Relay setting

    Can anyone help me how to compute the relay pick up, time delay and instaneous setting, to tell you the truth I dont know how to deal with it. Hope you can help. Thanks. S4-S1-SA, upstream. S4: CT Ratio 1000/5, Full load amps: 710 Amps,SCA-3p: 21,208Amps S1: CT Ratio 2500/5, Full load amps...
  6. 22574

    Transformer testing

    For power transformer oil filled.
  7. 22574

    Transformer testing

    Can you suggest what is more advantage or helpful in Transformer testing, doing insulation resistance test or insulation power factor test. Thank you.
  8. 22574

    LG and LL fault

    Hi, Anyone can provide me some formula or computation why a L-G fault is higher that L-L fault in distribution system mostly with XLPE feeders? Existing Transformers are solidly ground. Thanks
  9. 22574

    Earth fault relay

    Hi Guys, I need a help in looking for a procedure on how to set an earth fault relay What are parameters needed, (eg. short circuit fault, etc..) Thanks.
  10. 22574

    How to test SEL 121G

    Hi All, We have a SEL 121G for lab use, but my problem is I dont how to test it, does anybody have test procedures on this relay using doble f6150?
  11. 22574

    Relay equipment Test

    How about comparing to DOBLE F6150?
  12. 22574

    Frequency Response Analysis (FRA)

    Hi Unclebob, We are using sfra for testing transformer, specially after a fault. I attached sfra traces from 3 identical 1-phase transformers that I tested. This is very interesting because the instrument reveals that one of the 3 transformer got problem after a...
  13. 22574

    Hydrogen in Transformer Oil

    Thank you all for your answers to me. I appreaciated it very much. But oldfieldguy your my MVP.. pabs
  14. 22574

    Hydrogen in Transformer Oil

    What is the effect of Hydrogen in tranformer Oil? How hydrogen form inside the transformer? I hope you can help me on this.. pabs
  15. 22574

    wire rope use in KRUPP crane

    Can anyone provide me supplier for the wire rope use in a KRUPP Crane. 80Tons, Capacity with 3/4" dia. I will appreciate your help.