A core balance ground ct connection was used in O/L in a Motor,
while residual ground CT connection was used for O/C at the secondary side of Transfomer going to the switchgear where the motor connected.
My question is, can I coordinate the two relays?
What is more sensitive during ground...
YES,
Pls see specs below:
Bus bar length per phase (6.260 mm)
- Diameter = 1704 mm
- Rated voltage = 17.5 KV
- Conductor material = Hard Aluminum
- Rated current = 4,170 A
- Test Voltage = 38 KV
- BIL = 95 KV
- Number of...
Can anyone help me how to compute the relay pick up, time delay and instaneous setting, to tell you the truth I dont know how to deal with it.
Hope you can help.
Thanks.
S4-S1-SA, upstream.
S4: CT Ratio 1000/5, Full load amps: 710 Amps,SCA-3p: 21,208Amps
S1: CT Ratio 2500/5, Full load amps...
Hi,
Anyone can provide me some formula or
computation why a L-G fault is higher that L-L
fault in distribution system mostly with XLPE feeders?
Existing Transformers are solidly ground.
Thanks
Hi Guys,
I need a help in looking for a procedure on how to set an earth fault relay
What are parameters needed, (eg. short circuit fault, etc..)
Thanks.
Hi Unclebob,
We are using sfra for testing transformer, specially after a fault.
I attached sfra traces from 3 identical 1-phase transformers
that I tested. This is very interesting because the instrument reveals that one of the 3 transformer got problem after a...