We have a new laser cutting machine being installed shortly.
We chose not to purchase their extraction system
as it is installed in the factory right next to the laser
and does not remove the odour.
We will also be cutting a considerable amount of stainless steel & this should definitely be exhausted outside. Unfortunately the agent does not have any spec on what the extraction package was.
It looks like a 1 metre x 1 metre x 2 metre high box with
plastic cartrige filters 6 - 9 on each face about 140mm dia & has pulse cycle, is for dry solids only
Agent recomends 4000 CFM & outlet is 225mm OD-this doesn't
sound right to me i think they mean 4000 CFH ?.
they don't have a presure spec, the cutting table is
3 metre x 1.5 metre grid & is sectioned into 4 or 5 zones
along the 3 metre way & extracts only on the zone were the cutting is taking place.
(A lot of laser shops we visted did not buy the extraction
system & just extracted straight out the roof.)
Anyway they want $20,000 USD for their system.
some advice would be appreciated
Steve
We chose not to purchase their extraction system
as it is installed in the factory right next to the laser
and does not remove the odour.
We will also be cutting a considerable amount of stainless steel & this should definitely be exhausted outside. Unfortunately the agent does not have any spec on what the extraction package was.
It looks like a 1 metre x 1 metre x 2 metre high box with
plastic cartrige filters 6 - 9 on each face about 140mm dia & has pulse cycle, is for dry solids only
Agent recomends 4000 CFM & outlet is 225mm OD-this doesn't
sound right to me i think they mean 4000 CFH ?.
they don't have a presure spec, the cutting table is
3 metre x 1.5 metre grid & is sectioned into 4 or 5 zones
along the 3 metre way & extracts only on the zone were the cutting is taking place.
(A lot of laser shops we visted did not buy the extraction
system & just extracted straight out the roof.)
Anyway they want $20,000 USD for their system.
some advice would be appreciated
Steve
RE: Bag house design for metal cutting laser
Based on the size of the system that you describe, the recommended flowrate of 4,000 cfm sounds reasonable. Check out this link. These guys manufacture dust collectors for these types of applications.
http://www.farrapc.com/
Good Luck.
Tom
RE: Bag house design for metal cutting laser
Fan volume in CFM/desired duct velocity in FPM = Cross sectional area of duct in sq. ft.
For a round duct,
(Sq root (4000/2500*144)/pi)*2
For a square duct,
Sq root (4000/2500*144)
All this being said, for efficient fume extraction, the design and location of the hood is important. Maybe this is why you say that the shop where you saw this set up, wasn’t getting good extraction.
Haggis
RE: Bag house design for metal cutting laser
Pay the man. Get the right stuff.
Else, find a tome on industrial toxicology, and look up 'metal fume fever' and related subjects.
Mike Halloran
NOT speaking for
DeAngelo Marine Exhaust Inc.
Ft. Lauderdale, FL, USA
RE: Bag house design for metal cutting laser
One of the things to look out for is chrome in stainless which varies with the SS type.
IF in USA EPA will have some concern over chrome and of course the dust. Then there is the politics with the neighbors ie "theyre killin us with chrome". I do not think just dumping the exhaust to ambient outside air is the proper answer. Basically you made the mess in your shop clean it up in your shop.
OSHA has regulatins for chrome also. I predict you should not have too much problem with these the smoke is going to be the major concern and issue.
I wonder if water spray and or electric precipitator would be better for you - eliminates cost of filters WITH other trade offs and expenses of course - ain't no free lunch - but that is cost of doing business.
Dan Bentler
RE: Bag house design for metal cutting laser
If you have no joy, post here and I will give you some other contacts or see if I can help you myself
.
Be careful to ensure you use an industry specialist as dealing with Dusts, gases and Chromates will come under ATEX in Europe. Too many times installations do not meet legal requirements.
You will also need to consider Duty of care act very carefuly and a full risk assesment must be carried out to identify potential hazards
You will also require minimum H13 HEPA filtration for Chromates. 99.97% @ 0.3 microns EN1822 or DOP testing with certificates - circa 2000/4000M3/hr
If you are allowing Chromates to contaminate your factory space you may also need a full cleandown - In particular Chromium VI
Regular testing of all personel must be undertaken for Chromates.
Chromates, in particular VI are class 1 carcnogens and are present in many metals, paint, primers etc etc - hence wearing full breathing equipment.
In addition Chromates are also absobed in the tear ducts.
I believe the USA are reducing the 8 hour allowable limit from 5mg to 1mg from Jan 06
Hope this helps