Poor Power Factor Effects
Poor Power Factor Effects
(OP)
I am a mechanical engineer with an electrical problem. The power calculation using amperage, voltage, motor power factor and efficiency when combined with pressure readings on the pump performance curve gives a flow whiich is 20% higher (5000 GPM) than other measurements indicate.
The overall power factor for the plant site is corrected to .99 using a couple of large 18,000 Hp motors designed for the purpose but the power factor may not be .99 where the 700 Hp motor is connected. In fact it could be as low as 0.80
Can my horsepower calculation be the apparent power rather than the real power which actually used by the pump? I measure 96 amps, use 4160 Volts and interpolate for motor pf & eff from the test report.
I'm using the formula hp=1.73*E*I*pf*eff/746. The motor test report indicated that at full load the values are E=4000V, I=100.7 amps, Eff=94.8, Pf=78.9, Syn speed=900 rpm, Slip @ fL=1.43.
How would a supply power factor of 0.80 affect the Hp calculation. It isn't accounted for anywhere?
Any help would be appreciated.
The overall power factor for the plant site is corrected to .99 using a couple of large 18,000 Hp motors designed for the purpose but the power factor may not be .99 where the 700 Hp motor is connected. In fact it could be as low as 0.80
Can my horsepower calculation be the apparent power rather than the real power which actually used by the pump? I measure 96 amps, use 4160 Volts and interpolate for motor pf & eff from the test report.
I'm using the formula hp=1.73*E*I*pf*eff/746. The motor test report indicated that at full load the values are E=4000V, I=100.7 amps, Eff=94.8, Pf=78.9, Syn speed=900 rpm, Slip @ fL=1.43.
How would a supply power factor of 0.80 affect the Hp calculation. It isn't accounted for anywhere?
Any help would be appreciated.
RE: Poor Power Factor Effects
To go directly to your question, any power factor correction should be irrelevant to your power calculation UNLESS the power factor correction capacitors are connected at a point downstream of where you measure your motor current. ie plant power factor correction capacitors have not effect. If Power factor correction capacitors (or surge capacitors) were switched connected near motor terminals such that they could be switched with the motor, and you measured current at the breaker, then those capacitors would effect your calculation. To summarize, assuming you have only power factor correction capacitors, then your formula for shaft horsepower should be shp=1.73*E*I*pf*eff/746 as you stated.
When faced with an apparent contradiction, you have to start looking at what you have assumed vs what you have measured, and also consider the accuracy of what you have measured.
For the electrical power calc, best case is to measure the current (try all three phases and use the average). Measure the voltage at motor terminals or if measured at some remote point upstream, then correct for the voltage drop along the cable (forgetting to do this can give you a few percent error).
It sounds like you have assumed a value of power factor from the test data... but power factor can be measured directly with a power analyser, or with any two-channel oscilloscope (need to determine phase angle between voltage and current). If you're hooking up at secondaries of PT's and CT's, then consider the phase-angle shift introduced here.
Motor efficiency... you're stuck there. No way to measure that. But as a double check on the motor power you can measure the speed of motor with tach. Then you can estimate output power from the slip as compared to nameplate... with correction for voltage^2 and estimated rotor temp---- see recent threat on estimating Power from slip... temperatre correction.
The fluid parameters are likely to have more errors, even if you measure them. You need to know densitiy of your fluid (varies with temp). You need to know flow... presumably you're measuring dp across some flow element (annubar, orifice, venturi etc) to estimate flow... if it has clogged than your dp has gone up and it looks like you're drawing more mechanical power than you really are. Have your gages been calibrated? A good independent check on the flow is to use ultrasonic flow measurement. Likewise you might consider whether your measurement of DP is accurate... is it directly across the pump? Is there an elevation difference between the two pressure taps? Have elevation differences from tap to gage been properly accounted for?
The large slip makes me want to doublecheck... this is not a wound-rotor motor is it?
For more ideas do a search of this forum on efficiency... it comes up every month or so
RE: Poor Power Factor Effects
One way to look at this is with a one line diagram. The main bus will be connected to the utility tranformer and will supply feeders to the loads in the plant (such as the 700hp pump motor) and to the pf correcting motors. The power factor of the main bus measured at the utility transformer may be 0.99. But, each feeder from that bus will have a current draw, and power factor, based on the load connected to the feeder. According to Kirkoff's Current Law, the sum of the feeder currents, each with different magnitude and power factor, will be the bus current at magnitude Ibus with a power factor of 0.99. Clearly for this to take place the feeders to the pf correcting motors will have a leading power factor to offset the lagging power factors of all of the inductive feeders.
This being the case, the equation you are using is valid with the motor power factor as the variable. However, when you look at the motor's nameplate data, you must understand that it is based on full load. The power factor and efficiency of an induction motor vary with load. As load decreases, power factor and efficiency decrease.
The manufacturer should be able to provide curves (or tables) showing how current, speed, power factor, and efficiency vary with load for your motor. You should try to get these as the improved accuracy of your calculation may clear up the discrepancy.
RE: Poor Power Factor Effects
Density of course changes with temperature and if temperature is varying among different points in your loop, that needs to be considered.
Density at the flow element must be known to determine either mass flow rate or volumetric flow rate from flow element dp.
Density at the pump must be known to determine fluid horspower delivered by pump.
If density at flow element differs from density at the pump, then you have to do your power calculation based on mass flow rate, since volumetric flow rate will differ at those two locations.
In determining a dp across the pump based on two pressure measurements.... I mentioned that the height of fluid between those pressure taps and the pressure meter plays a role which must be accounted for. Also the temperature of the fluid in the sensing lines determines density of that fluid and impacts the indicated pressure.
RE: Poor Power Factor Effects
(1)- We manufacture pulp for papermaking. There are no capacitor banks for power factor correction but in the plant design we knew that without any correction the overall Pf would be ~0.80 Therefore when we purchased the main refiner motors (~18,000 Hp) they were designed to give us the correction required to offset the inductive load from the other motors (~150) located elsewhere in the plant. When you look at the single line diagram there is one main feeder at 13.6 KV supplying the large 18,000 Hp motors and individual 4160 V & 600V feeders to the rest of the plant.
(2) - The manufacturer curves for centricleaners and plant mass balances agree but the capacity from the pump performance curve using Hp and discharge pressure indicates an additional 20% or 5000 GPM. The cenricleaner curves are used everywhere for pump sizing and a 20% error would mean major mistakes in pump sizing throughout the industry, which is not the case. In addition, if our mass balance calculations for the entire plant were out by 20% for the past 9 years, it would be embarassing. This leaves the pump flow calculation as the main source of error. The pressure readings were obtained from pressure transmitters with manual gauges used to confirm the readings. That leaves the power reading as the suspect.
(3) - Next week we will rent a more sofisticated device to measure the amps, voltage, & power factor. Should the pf obtained from the meter reading be the resultant of the plant plus the motor or simply the motor pf from the manufacturers test report at that load?
(4) - I put a strip chart recorder and recorded 96 amps for 12 hours. Just a straight line close to the full load value.
At this point in time we are concentrating on the power calculation. The ramifications of a low pf supply is not fully understood by me.
RE: Poor Power Factor Effects
Your large synchrnous motors, for the purposes of this discussion can be treated the same as capacitors. Namely, if the current flowing to those sync motors is NOT flowing past the point where you measure your inducation motor current (which I understand to be the case), then they are irrelevant to the calcualtion of power in your motor.
The only thing your motor knows is that you give it a voltage. Then the motor draws a current which will be displaced by a certain power factor angle from the voltage you gave it. That power factor angle depends only on the motor (and of course the mech load on the motor and the voltage magnitude), but it does NOT depend on any other electrical load or power factor correction device in the plant.
When you talk about a power factor, it is the angle between voltage and current and a certain point in your power distribution system. The real power flowing at that point in the distribution system with be P=|V||I|*cos(theta) where theta is angle betwee that V and that I.
We can apply the equation either at the plant level or at the motor level, but we will be using a different differnt V a different I and a different cos(theta) and calculating a different power P. There is really no reason to bring the plant power factor into any discussion of the motor power factor.
The syncronous motors affect the plant power factor, In effect, they will increase cos(theta) to 1, so you can deliver the same P with lower |I|. The same equation is also true at the motor terminals where we are using a differnt V a different I and a different cos(theta). Once you give the motor a |V|, it will determine it's own |I| and cos(theta) REGARDLESS of what is going on at the plant level. Sorry for repeating myself... maybe repetition will make up for any lack of clarity
Can you tell us whether the power calculated electrically is more or less than the power calculated mechanically? ie does it seem like we're getting free energy or does it seem like we're losing energy somewere?
If it seems like we're losing energy, then the following types of items might be investigated:
Rotor bar problems
Voltage at motor terminals is lower than voltage at poitn of measurement due to volt dro in the motor cables.
Motor power factor is low due to core problems.
Pump has wearing ring problems or unmetered bypass flow (whoops sorry ... back to electrical).
harmonics in the system cause |I| or |V| to be larger for the same power.
Motor is running hot... more I^2R losses (but not that 20% of output more).
Electrical measurement errors - see below.
If it looks like we're gaining energy, the list is much shorter. I can't particularly see efficiency or power factor improving that dramatically, even at reduced load. Off-hand all that comes to mind is measurement errors:
Calibration of ammeter
calibration of voltmeter
Unbalanced voltages or currents and you read the highest one.
Perhaps you have assumed 4kv and your actual voltage is higher?
Perhaps you are measuring on the secondary of a voltage or current instrument transformer which has a ratio error... or you have mis-read the ratio?
OK, before I go any further, which case are we looking at?
RE: Poor Power Factor Effects
RE: Poor Power Factor Effects
be hp= 1.72*E*I*pf/eff*746 ??
It's Friday and I'm tired so I may be off.
RE: Poor Power Factor Effects
1.73 is closer to the sqrt(3) than 1.72. Sqrt 3 is the actual number.
Motor efficiency should go in the numerator (remembering that the P we are calculating is shaft horsepower output delivered by the motor).
I'm pretty sure that the 732 goes in the denominator.
RE: Poor Power Factor Effects
RE: Poor Power Factor Effects
We have two identical pumps but only one is operated at any given time, the other is a spare. One pump has a 700 Hp motor & the other has a 900 Hp motor. The reason for the 900 Hp had to do with expansion. Since both pumps have the same size impeller they find a point on the curve to operate and only take as much power as required. That is the case with the measurements. The Hp consumed is about the same after you apply the different eff & PF from the manufacturers test report for the given current flows.
One other thing, they measured one current and calculated a percent motor load using the full load amperage number, which checked out on the DCS. After that they just took % motor load readings for any given flow and calculated the HP. I believe DCS assumes the % power taken from the CTs follow a linear line when in reality it could be a curve. This will be checked next week.
Thanks for the feedback & I'll update things next week after another round of tests are complete.
RE: Poor Power Factor Effects
In your case where motor input power corrected for motor efficiency and power factor is still greater than pump output power corrected for efficiency, almost everything discussed above holds as possible source of error. It'll be tough to narrow it down from this end, maybe you have a better feel where to start. For instance, have we been measuring mechanical power all along and it suddenly went down. Or have we been measuring electrical power and it suddenly went up.
Broadly, the 4 types of factors can be divided into:
#1 - Errors in measuring mech power out (discussed above).
#2 - Errors in measuring elect power out (discussed above)
#3 - Things that make mechanical efficiency go down (worn wearing rings, debris in motor etc)
#4 - Things that make motor efficiency or p.f. go down (hi temperature, broken rotor bars, high voltage which causes low power factor).
RE: Poor Power Factor Effects
For example at 0, 25, 50, 75, 100, & 125 % full load.
Current= 46.5, 51.6, 64.0, 80.9, 100.7, 122.8
Efficiency= 0, 90.1, 93.9, 94.8, 94.8, 94.5
Power Factor= 4.2, 40.5, 62.7, 73.7, 78.9, 81.1
Slip= 0, 0.33, 0.68, 1.04, 1.43, 1.86
The Locked rotor torque= 129.9
Locked rotor current = 656.5 amps
Breakdown torque = 264.3%
Pull up torque = 103.9%
The no load test had values of:
Volts=4000
Amperes=46.5
Watts=13500
A couple of years ago they put a full size impeller in the pump to maximize the flow. According to the pump performance curves it should not have overloaded but it did and the impeller had to be removed. It appears that the power we measure is higher than expected. Either we read the wrong value and use that value for control purposes or the excess power is being dissipated as friction or wear. The power, if measured correctly, is being consumed, which is the reason I started thinking about the apparent, real, & imaginary components of power. I was hoping to explain the difference by saying I measured the apparent power when in actual fact I should be subtracting the imaginary component to get the real power.
Very interesting challenge which will get solved. Thanks for the input.
RE: Poor Power Factor Effects
(Pout (HP) = Pin(kW)*eff/0.746), rather than extrapolate from a single phase current reading. Should be worth the investment in a 2-element watt transducer to get the right numbers.
RE: Poor Power Factor Effects
The 96A reading is for all practical purposes equal to the motor full load, so the values of power factor, efficiency, and slip should match up between the motor in service and the manufacturer's data. Power factor and efficiency are difficult to measure, but slip isn't. I would recommend measuring the shaft speed of the motor and comparing it to the full load slip in the data. By the way, if I am reading the slip data right you are saying a slip of 1.43% which is not very much at all. Either way, if you can determine that the amps and slip match the full load data, then you can make a safer assumption of the motor output being full load.
Measure the shaft speed and see what you get. If it is running at a slip of 1.43%, or at 887 rpm, then you may follow with the assumption that bhp at the pump input is correct and the losses are downstream of the motor (in the pump etc.). If the motor is running at a lower value of slip (at a higher speed) than indicated by the current, then you may follow with the assumption that the bhp input is less than indicated by the current and the problem is in the motor or upstream of the motor.
RE: Poor Power Factor Effects
RE: Poor Power Factor Effects
power = I * E * 1.732 * pf * eff
This is in Watts. Divide by 746 for horsepower. Efficiency cannot exceed 1.0, nor can power factor.
I think the discussion is only being complicated by the plant pfc synchronous motor references. Best thing is to get a cheap power meter to measure the power factor and apparent kw close to the motor terminals. Please.... I realize "apparent kw" is poorly worded.
Anyway, since the FLA appears to be in the ballpark, I think a harmonic analysis (FFT) needs to be done to determine how much trash is on his line. Chances are this motor is not causing it, but I wouldn't be surprised to find some motor drives or precipitators or similar harmonic source on the same line... What about it matador? If this is the case, you're reading a lot of amperage noise that isn't contributing to anything but the errors in your calculations.
I've been in a few paper mills and pulp plants, and I'd guess E-P's 7-27 comment on harmonics is being overlooked in this case. Break out an oscilloscope for a quick-and-dirty check. If you don't see sinewaves off some HED's/current probes, this is the right track to follow. If you do see sinewaves, then I never suggested this, and I'll blame it on rhatcher when he's not looking.
Don, who may not always be right but is always opinionated
RE: Poor Power Factor Effects
I have had a chance to print this out and read it more carefully. A couple of questions.
I did not see the differential pressure across the pump. Did you state what it is? Sorry if I missed it. The efficiency of you system is Pump efficiency x Motor efficiency. Pump efficiencies can run as low as 30% for things like trash pumps. The loss in motor efficiency shows up as heat in the motor. The loss in pump efficiency shows up as heat in the water.
5000 GPM is 41,700 lbs of water moving through the pump per minute. One horsepower is 42.4 BTU/ min. I calculate that one lost Horsepower would raise 41,700 lbs of water about 0.001 degrees F. Someone please check me on that. You could be loosing power as heat in the pump and the temperature rise in the water may be very slight ( to small to measure with instruments of normal range).
I do know that pumps can be very good water heaters. The hydro test on BWR pressure vessels was done by running the recir pumps- It didn't take long to get a very large vessel up to 1000 degrees and 800 PSI.
RE: Poor Power Factor Effects
Measurement errors (power or preesure) would move the curve left or right. In this case we are hoping to measure less power which will give us less flow for a given pressure.
We rented an instrument and it was damaged when it arrived at the site. A replacement unit has been shipped.
RE: Poor Power Factor Effects
The meter will stay on all night. One set of reading are:
Phase Voltage Current Measured KVA Watts Measured (W) KVAR Measured PF Measured
A 3759 101.3 381100 194100 328000 0.51
B 4821 97.83 471600 180100 435000 0.38
C 4414 101.9 450100 215600 395000 0.48
Totals 1300000 589900 1159000 0.45
The motor PF should be .78 for the load & we are getting an average of .45 Comments please.
RE: Poor Power Factor Effects
If the readings are correct, then you are operating at approximately 8% above rated voltage (average) with a 13% voltage unbalance. The overvoltage explains some of the drop in power factor, although the drop from .78 to .45 seems extreme, even considering one phase is 20.5% above rated. This overvoltage should also increase the slip by a noticeable amount - this can be verified by measuring shaft speed.
The 13% voltage unbalance, if correct, is mind-boggling on an MV system. Motor operation above 5% unbalance is definitely not recommended. However, I doubt this reading is correct because there should be a much greater current unbalance, whereas the measured phase currents are fairly balanced. A voltage unbalance of the level indicated by the measurements would cook this motor in short order under full load.
Check your meter and connections and post what you find.
RE: Poor Power Factor Effects
IF the reading are correct, then as redtrumpet said, the voltage unbalance and overvoltage is totally unacceptable. It would certainly cause a dramatic reduction in efficiency and power factor which could explain your initial symptoms. More importantly, your motor(s) are in grave danger of overheating and damage. For unbalanced voltage conditions, simple phase overcurrent protection does not protect the motor. (The effects of negative sequence currents on the rotor are much more severe than would be predicted by the magnitude of the current in any one phase.) The overvoltage condition cause extra heating in the core and also increases the stress on the insulation.
In summary, IF it's an actual condition it needs to be fixed pronto. IF not, then perhaps correcting the voltage connections will bring the other readings into line.
RE: Poor Power Factor Effects
RE: Poor Power Factor Effects
With those sorts of numbers has the protection gear complained???
Are we sure we don't have some US gallons fighting imperial gallons??
If we use an accuratish meter test the terminals test the current with a tong do they verify (within a small order of accuracy) the super test rig?
I understand your confidence in your mass balance (and draw ups?) But we Know x amps y volts are going in. except for pf they have to go out and the pump is the place.
How is the mass balance calculated could there be the use of say dp flow meters or zero suppressed dp level meters. Are youre slurry lines purged? I don't mean to sound negative but I have a hunch that this is not just the motor. And I mean just a hunch.
Please keep us informed this IS really interesting
Don
RE: Poor Power Factor Effects
Its nearly midnight here and I did it again. Tongs on a 4000v conductor - sorry.
New thought reading the early posts again. There is a 700 hp motor and a 900hp motor with same pump service. Yes the pump will only do the work it wants to do but the two motors ARE going to have different numbers. The pf of the 900 should fall.
Now we have pf correction upstream of the motors and a number of transformers in between. My factory has a pf of.98 ~.98 at 415V (1000amp) using a cap bank and controller. this fed from the util transformer 20 meters away.
BUT I'll bet that the power factor in the street upstream of that trani aint .98
I could be wrong but its a thought
regards Don
Ps I have never had any luck getting an accurate indication of amps onto a DCS. Always the transducer or ct or calibration or somebloody thing aint quite right.
This is in petro chem and slurry type system with some pretty expensive gear.
RE: Poor Power Factor Effects
I called the company where we rented the meter to have them check the calibration when they get it back in the office. The plan is to rent another meter and take another set of measurements. If the voltage unbalance really exists we have some serious problems.
I'll update things again when I have more information from the new test data.
Thanks everyone for your input.
RE: Poor Power Factor Effects
There are a few other things interesting about this problem. Hopefully I won't detract from the straightforward plan identified above if I go off on a few tangents.
I've never worked on a motor that had current/voltage imbalance before and I havent read a whole lot about it.
One question that is often considered is whether a system voltage balance is causing the motor to draw unbalanced currents (supply problem), or whether imbalanced motor currents are creating a voltage imbalance (motor problem).
In your case the voltage imbalance magnitude far exceeds any current imbalance, which seems to suggest a system problem vs motor problem. Likewise you see similar voltage imbalance regadless of which motor is running... once again points to supply problem instead of motor problem.
As Redtrumpet noted, it seems surprising that a 13% voltage imbalance gives rise to only 1.5% current imbalance. I was always under the impression that the current imbalance should be several times as large of the voltage imbalance. I base this on the fact that motor negative sequence impedance is often assumed equal to starting impedance (for fault calculations... per IEEE Brown book) which is 5-7 times lower that positive sequence impedance. This would seem to imply the current imbalance should be perhaps 6 times as much as the voltage imbalance. You've got it going the other way... current imbalance on the order of 1/10 of voltage imbalance.
I'm assuming that it's easy to make errors in measuring phase and absolute magnitude, but it's very unlikely to make errors that change the computed value of voltage or current imbalance... (as discussed above this is simple comparison of three magnitudes measured in similar manner with presumed similar errors).
I'm sure that there may be a large component of the current which is excitation current due to the overvoltage. That contributes a component of current that becomes larger as voltage increases.
Also interesting to see that the lowest current occurs at the terminal with highest voltage (to ground).
Does anyone know in general whether the phase with highest voltage sees the highest current when problem is caused by supply voltage imbalance? (I do believe that the phase with the highest voltage has the lowest current when problem is due to motor... but in that case no reason for voltage to ever increase above nominal).
All of this is to say that the motor current magnitudes dont' seem to fit the simple explanation of a supply system voltage imbalance (can anyone explain them?)... although I'll admit I've never seen a supply imbalance and don't know exactly what it should do to the currents. Nevertheless the imbalanced supply system voltage measurements clearly need to be first line of investigation. Just try to keep an open mind along the way.
RE: Poor Power Factor Effects
The medium voltage and attached larger loads do not have this problem so frequent since the large three phase loads are manufactured to be fairly accurately balanced in load to avoid very costly consequences.