Wind Load on Pipe Rack

Wind Load on Pipe Rack

Wind Load on Pipe Rack

(OP)
I have a long, five- tier structural steel pipe rack supported on braced bents spaced about 30 ft c/c. Bent width is about 20 ft. The total height of the structure is about 38 ft. There is a possibility that the owner may decide to place cladding on both sides of the upper 18 ft of the pipe rack in order to hide the piping, etc from view.  There will be no roof but, of course, the top level may or may not be loaded up with pipes, cable trays, etc.

Question: What is the wind load? Do I consider there to be two separate walls, each subject to positive wind pressure? Will the windward wall offer any shielding to the leeward wall?

Any advice or references would be appreciated.

Frank Hartzell
Jacobs Engineering
Conshohocken, PA
frank.hartzell@jacobs.com

Replies continue below

Recommended for you

RE: Wind Load on Pipe Rack

Frank...a couple of comments:

When the rack is loaded, the net wind load will likely not be critical.  

When unloaded, with the panels at the top, the lateral net wind load will likely be at its most critical.  In general, the windward side of the structure would have a factor of about 1.25 to 1.50 and the leeward side would have a -0.75 to -1.0, therefore both acting in the same direction.  If the top of the rack is open, you would need to consider windward and leeward pressure on each of the panel walls, as the wind could "dip" over the top of the leading panel wall and impact the lagging wall, thus exerting pressures on both.  This, I believe, answers your shading question.

You might also check the rack with only a few pipes on it, as this could conceivably give you a higher wind pressure from the side, though likely the dead load of the pipes will be adequate to stabilize for overturning.

Ron

RE: Wind Load on Pipe Rack

Check your building code for wind load requirements on Components and Cladding.  Then, like Ron said, you may have to consider pressure on one face and suction on the other acting at the same time.

RE: Wind Load on Pipe Rack

Using ASCE 7-95 as the guide to most building codes your threshold for Components and cladding is a trib area of 750 square feet.  A 30 spacing of bents would only need to be 25 feet high to meet this.  You can use the main wind force resisting system to determine your total load.  When calculating this, you can leave out the internal wind coefficient, GCpi, because you have no internal pressure.  Also look to see if you could qualify as an open structure since your cladding could concievably be on one side.  Finally don't forget to check the column for overturning compression, where the worst case would be fully loaded.
Hope this helps.

RE: Wind Load on Pipe Rack

If there is a cladding 18' deep, it certainly will provide a lot of
shielding to a similar cladding 20' on the leeward side. You
should consider a shape coefficient of 1.5 for the windward
cladding. The shielding coefficient for your case should be
available in some codes. (I know Indian Standard has, others
should have; and some texts should. Sorry, I get no time for
search these days!). It would be of the order of 2/3, and your
total force would be about 2 times the basic wind pressure
times the area.

Windward = 1.5 * force
Leeward = (1 - 2/3) * windward = 0.5 * force
Total = 2 * force, where force = pressure * area

The load on the elements not covered by the cladding should be
considered separately!

HTH,

M. Hariharan

RE: Wind Load on Pipe Rack

I have found that wind loads and seismic loads can often dominate the design for pipe racks but then my designs are often in cyclone (hurricane) regions and/or seismic regions.
The sheeting on the windward side should shield the pipes and leeward sheeting and will probably be in your wind loading code.
You will have to check different load combinations to see which is the most critical for design, including uplift on footings.
Pressure coefficients are likely to be different between your code and mine so I won't quote any.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close