I have a long, five- tier structural steel pipe rack supported on braced bents spaced about 30 ft c/c. Bent width is about 20 ft. The total height of the structure is about 38 ft. There is a possibility that the owner may decide to place cladding on both sides of the upper 18 ft of the pipe rack in order to hide the piping, etc from view. There will be no roof but, of course, the top level may or may not be loaded up with pipes, cable trays, etc.
Question: What is the wind load? Do I consider there to be two separate walls, each subject to positive wind pressure? Will the windward wall offer any shielding to the leeward wall?
Any advice or references would be appreciated.
Question: What is the wind load? Do I consider there to be two separate walls, each subject to positive wind pressure? Will the windward wall offer any shielding to the leeward wall?
Any advice or references would be appreciated.
Frank Hartzell
Jacobs Engineering
Conshohocken, PA
frank.hartzell@jacobs.com
RE: Wind Load on Pipe Rack
When the rack is loaded, the net wind load will likely not be critical.
When unloaded, with the panels at the top, the lateral net wind load will likely be at its most critical. In general, the windward side of the structure would have a factor of about 1.25 to 1.50 and the leeward side would have a -0.75 to -1.0, therefore both acting in the same direction. If the top of the rack is open, you would need to consider windward and leeward pressure on each of the panel walls, as the wind could "dip" over the top of the leading panel wall and impact the lagging wall, thus exerting pressures on both. This, I believe, answers your shading question.
You might also check the rack with only a few pipes on it, as this could conceivably give you a higher wind pressure from the side, though likely the dead load of the pipes will be adequate to stabilize for overturning.
Ron
RE: Wind Load on Pipe Rack
RE: Wind Load on Pipe Rack
Hope this helps.
RE: Wind Load on Pipe Rack
shielding to a similar cladding 20' on the leeward side. You
should consider a shape coefficient of 1.5 for the windward
cladding. The shielding coefficient for your case should be
available in some codes. (I know Indian Standard has, others
should have; and some texts should. Sorry, I get no time for
search these days!). It would be of the order of 2/3, and your
total force would be about 2 times the basic wind pressure
times the area.
Windward = 1.5 * force
Leeward = (1 - 2/3) * windward = 0.5 * force
Total = 2 * force, where force = pressure * area
The load on the elements not covered by the cladding should be
considered separately!
HTH,
M. Hariharan
RE: Wind Load on Pipe Rack
The sheeting on the windward side should shield the pipes and leeward sheeting and will probably be in your wind loading code.
You will have to check different load combinations to see which is the most critical for design, including uplift on footings.
Pressure coefficients are likely to be different between your code and mine so I won't quote any.