Insulation resistance, winding resistance & PI
3

Insulation resistance, winding resistance & PI

Insulation resistance, winding resistance & PI

(OP)
Can anyone recommend good reference material ie books and/or websites on insulation,insulation resistance testing, etc.
I have the following questions in particular (this applies to testing motors)
1. What percentage variance is acceptable for winding resistance results for the three phases
2. What PI value is deemed acceptable? 2.0?
Most of the motors are 415V motors, with a handful at 3.3kV.
Look forward to comments, answers,etc. thanks.
Replies continue below

Recommended for you

RE: Insulation resistance, winding resistance & PI

2
The Bureau of reclamation has some outstanding info.  See:
http://www.usbr.gov/power/data/fist/fist3~1/3~1_cont.htm

IEEE 43-2000 is the standard for insulation testing of rotating machines.

According to IEEE 43-2000, 2.0 if the minimum limit for motors with insulation Classes B, F, H.  For class A (only very old motors, the limit would be 1.5).  Also if you have pre-1970's motors with asphaltic insulation systems, I think there may be other limits applicable.

EPRI recommends a maximum 1% winding resistance "imbalance" among the three readings, which they define as
imbalance = (Max-Min)/average.  That value may be a little conservative, so failure to meet that criterion doesn't necessarily mean the motor has a problem, only that you need to investigate some more.

RE: Insulation resistance, winding resistance & PI

Good answer electricpete. I would like to add that one must be careful with winding resistance as it is very temperature dependent. A motor with a heater(s) in the stator will almost certainly give erroneous readings as the location of the heaters will probably affect the resistance of one or two phases as opposed to equally affecting all three.

Also, a more liberal (maximum) acceptable value for winding variations, whether inductance or resistance, is +/10% of the average value.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close